hi all I've got my first consumer unit change to do as I'm using this as my first nic assessment. My question is when doing my ir test the whole house is on led downlights about 30 of then plus under kitchen 12v led and a lot of sub sockets, will all,of theses need to be disconnected to do these test. Also do I need to do r1+r2 on every downlight.

Any advice is much appreciated as this is my first nic assessment after this change.

Thanks
 
I don't recall stating which boxes I fill in, I just agreed that Zs-Ze=R1+R2.
It doesn't really. It can verify cpc continuity in an already energised installation which is fair enough. But some people are advocating noting down a reverse engineered value under the dead continuity test boxes which is frankly a nonsense.
 
It still doesn't explain why you feel the need to fill in a box for something which you are stating that you have not tested and have also stated that you do not need to test. If that is your position then do not fill the box for it in! To do so is both misleading and pointless.

Totally agree. My certs usually have loads of unfilled boxes. If I didn't check or measure something, it doesn't go in the box. And if I measure something once it only gets written down once. So, for RCD times, the values go on a line for the RCD and not on the lines for every circuit it protects.
 
So, for RCD times, the values go on a line for the RCD and not on the lines for every circuit it protects.
Personally for an RCCB I list the times next to each protected circuit rather than list the RCCB separately on a line of its own. But so long as what you have is clear then I don't have a problem with it being done that way.
 
It doesn't really. It can verify cpc continuity in an already energised installation which is fair enough. But some people are advocating noting down a reverse engineered value under the dead continuity test boxes which is frankly a nonsense.
It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.
 
It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.
A calculated Zs will err on the side of safety. To reverse engineer the R1+R2 will err on the side of danger. It also serves no purpose when you are verifying cpc continuity on an already energised installation with live (Zs) testing. Filling in a box simply because it exists on the form has no merit when you are excluding dead continuity tests. If you are excluding it then exclude it!
 
It isn't necessarily nonsense, where there are no parallel paths the reading is probably quite accurate. This isn't much different to people calculating Zs which I have seen recommended on this forum where a live reading should be obtained. For example dead testing R1+R2 then adding on Ze.

It is entirely different to calculating Zs.
Calculating Zs from (R1+R2)+Ze gives a value based on two measured readings, so it is not really calculated, merely an addition of measured values. It also gives a worst case scenario, a maximum figure for Zs for that circuit without any connected parallel paths to earth that, if compliant, can only mean that a live (connected) Zs will be less and therefore also comply with disconnection times. That is the reason this value is permitted to be entered as a value on a schedule of test results to BS7671

Calculating R1+R2 from Zs by subtracting Ze accounts for no connected paths and therefore will not be accurate. As Risteard says, this is an valid enough method of verifying continuity of protective conductors on an already energised circuit, but not a valid way of obtaining a reliable value of R1+R2.
 
Joking im not. Zs-Ze does equal R1+R2, its a very popular method of testing and not to mention quicker.

That is not a method of testing, it is a method of calculating an estimated value.

It is not a viable method of attaining a value for the continuity of the CPC, for initial verification it is a requirement that the R1+R2 or R2 be measured prior to making a circuit live,
 
That is not a method of testing, it is a method of calculating an estimated value.

It is not a viable method of attaining a value for the continuity of the CPC, for initial verification it is a requirement that the R1+R2 or R2 be measured prior to making a circuit live,

not sure thats fact dave, im sure it states, measure or calculate. If the earth path was compromised the zs reading would show this so its no different to R1+R2 and saves loads of time.
 
not sure thats fact dave, im sure it states, measure or calculate. If the earth path was compromised the zs reading would show this so its no different to R1+R2 and saves loads of time.

If you are not sure that what someone says is a fact it is customary to quote a fact to back up your contradictory viewpoint.
 

Reply to Consumer unit change testing in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
282
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
792

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top