i have been asked to replace a consumer unit and have seen that the main bonding to water and gas are only wired in 6mm. does this have to be upgraded to 10mm so that it meets current regs as its a tncs system. thanks.
 
Time to get out your big green book! BS 7671 131.8 is worth reading and understanding in such situations.

A call to your scheme technical helpline would also be a sensible step (after you've reviewed 131.8).

Hope this helps
 
Last edited by a moderator:
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.
 
Time to get out your big green book! BS 7671 131.8 is worth reading and understanding in such situations.

A call to your scheme technical helpline would also be a sensible step (after you've reviewed 131.8).

Hope this helps

I do love a number chase - lol

Just to add, 543.1.3, then 543.1.4, then onto 544.1.1 but don't forget to check 531.1 which will lead you to 411
 
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.

have to use this on lot of properties lately as company dont want existing bonding altered which i wasnt happy about so i now quote above on test sheet for qs to sign (providing bonding checks out of course)
 
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.

Dam, its Jan 21st and I haven't got this far in the new green book.
 
Last edited by a moderator:
is that regulation a direct quote from new bgb lenny? (dont own one yet, single copy held in boss office for reference)


No, not exactly.

In BS7671, 2008, 131.8 basically stated that no addition or alteration should be carried out unless the earthing & bonding requirements were adequate.

In BS7671, 2011, 131.8 has now become 132.16 and is worded slightly differently.

The guidance I referred to was from the ESC guide on CU upgrades were a TN-C-S earthing system is present.


This is the actual text......


"The minimum main bonding conductor sizes specified in Table 54.8 were first introduced into the Electricity Supply Regulations on 1 October 1988. Smaller minimum sizes were accepted by some electricity distributors prior to that date, but the sizes given in Table 54.8 were introduced to reduce the likelihood of main bonding conductors overheating due to the PME network circulating currents which the conductors may have to carry continuously or for long periods. Distributors may specify larger main bonding conductor sizes where local network conditions require this.


Where a designer finds, in an existing installation where PME conditions apply, that the main bonding conductors have a csa of say 6 mm2 rather than 10 mm2, the designer may, having carefully considered all the circumstances, conclude that the deficiency does not pose a significant risk to the users.

For example, if there is no evidence of overheating of existing main bonding conductors and terminations, it may be reasonable to assume that the existing arrangements are adequate for any network circulating current (unless the main bonding conductors were only recently installed). However, the deficiency must be recorded, together with the reasons why the installer has concluded that the deficiency does not pose a significant risk to the users.

It should be noted that the non-correction of departures from the requirements of BS 7671 is not an option in a new installation or for the rewire of an existing installation".
 
Last edited by a moderator:
You mention 'network circulating currents' in bonding cables. Is there generally current circulating in bonding conductors in PME systems then? I was under the impression that the only time current would flow in bonding conductors would be under fault conditions.
 

Reply to consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net

Similar threads

During a new CU installation does the bonding for the gas and water also have to be upgraded to the latest regulations or just tested/ inspected?
Replies
0
Views
149
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
649

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top