i have been asked to replace a consumer unit and have seen that the main bonding to water and gas are only wired in 6mm. does this have to be upgraded to 10mm so that it meets current regs as its a tncs system. thanks.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net
Time to get out your big green book! BS 7671 131.8 is worth reading and understanding in such situations.
A call to your scheme technical helpline would also be a sensible step (after you've reviewed 131.8).
Hope this helps
It's 132.16 now.:stooge_moe:
Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.
It's 132.16 now.:stooge_moe:
Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.
Youre well ahead of me still....no green book evenDam, its Jan 21st and I haven't got this far in the new green book.
Youre well ahead of me still....no green book even
is that regulation a direct quote from new bgb lenny? (dont own one yet, single copy held in boss office for reference)