P

payney 0

i have been asked to replace a consumer unit and have seen that the main bonding to water and gas are only wired in 6mm. does this have to be upgraded to 10mm so that it meets current regs as its a tncs system. thanks.
 
You mention 'network circulating currents' in bonding cables. Is there generally current circulating in bonding conductors in PME systems then? I was under the impression that the only time current would flow in bonding conductors would be under fault conditions.


Courtesy of National Grid.......

[h=1]Interrupted neutral conductor[/h][h=2][/h]We explain here how the system of protective multiple earthing used in the UK produces net currents which are the main source of magnetic field in most homes. But the net current can be much bigger if pme is combined with an interrupted or broken neutral conductor.
Consider first the situation with an intact neutral conductor:
[ElectriciansForums.net] consumer unit change with undersized main bonding.

The live current has to flow in the distribution cable but some of the neutral current can divert out of the cable. This is what produces the net current. The amount of the neutral current which diverts is proportional to the impedances. Suppose the earth connection has an impedance (or resistance) 10 times bigger than the neutral current. Then 10% of the neutral current will divert and the net current is 10% of the neutral current.
Now consider what happens if the neutral conductor is broken for some reason:
[ElectriciansForums.net] consumer unit change with undersized main bonding.

None of the neutral current can return in the cable so it all has to divert into the earth (or through a link box into an adjacent circuit). The net current is now 100% of the neutral current.
 

Reply to consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net

Similar threads

During a new CU installation does the bonding for the gas and water also have to be upgraded to the latest regulations or just tested/ inspected?
Replies
0
Views
151
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
650

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top