P

payney 0

i have been asked to replace a consumer unit and have seen that the main bonding to water and gas are only wired in 6mm. does this have to be upgraded to 10mm so that it meets current regs as its a tncs system. thanks.
 
You mention 'network circulating currents' in bonding cables. Is there generally current circulating in bonding conductors in PME systems then? I was under the impression that the only time current would flow in bonding conductors would be under fault conditions.


Courtesy of National Grid.......

[h=1]Interrupted neutral conductor[/h][h=2][/h]We explain here how the system of protective multiple earthing used in the UK produces net currents which are the main source of magnetic field in most homes. But the net current can be much bigger if pme is combined with an interrupted or broken neutral conductor.
Consider first the situation with an intact neutral conductor:
[ElectriciansForums.net] consumer unit change with undersized main bonding.

The live current has to flow in the distribution cable but some of the neutral current can divert out of the cable. This is what produces the net current. The amount of the neutral current which diverts is proportional to the impedances. Suppose the earth connection has an impedance (or resistance) 10 times bigger than the neutral current. Then 10% of the neutral current will divert and the net current is 10% of the neutral current.
Now consider what happens if the neutral conductor is broken for some reason:
[ElectriciansForums.net] consumer unit change with undersized main bonding.

None of the neutral current can return in the cable so it all has to divert into the earth (or through a link box into an adjacent circuit). The net current is now 100% of the neutral current.
 

Reply to consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
561
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
998
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
935

Similar threads

During a new CU installation does the bonding for the gas and water also have to be upgraded to the latest regulations or just tested/ inspected?
Replies
0
Views
245
It's the only one robust enough to take a SWA gland and supply sized SWA cable. The only one that I've ever had fail was a twin row one on a...
Replies
4
Views
230

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top