consumer unit change with undersized main bonding. | on ElectriciansForums

Discuss consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net

P

payney 0

i have been asked to replace a consumer unit and have seen that the main bonding to water and gas are only wired in 6mm. does this have to be upgraded to 10mm so that it meets current regs as its a tncs system. thanks.
 
Time to get out your big green book! BS 7671 131.8 is worth reading and understanding in such situations.

A call to your scheme technical helpline would also be a sensible step (after you've reviewed 131.8).

Hope this helps
 
Last edited by a moderator:
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.
 
Time to get out your big green book! BS 7671 131.8 is worth reading and understanding in such situations.

A call to your scheme technical helpline would also be a sensible step (after you've reviewed 131.8).

Hope this helps

I do love a number chase - lol

Just to add, 543.1.3, then 543.1.4, then onto 544.1.1 but don't forget to check 531.1 which will lead you to 411
 
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.

have to use this on lot of properties lately as company dont want existing bonding altered which i wasnt happy about so i now quote above on test sheet for qs to sign (providing bonding checks out of course)
 
It's 132.16 now.:stooge_moe:

Guidance suggests that if the existing 6 mm bonding connects all the extraneous-conductive-parts to the main earthing terminal, has been in place for a significant time and shows no signs of thermal damage, then it may not be required to upgrade it.

Dam, its Jan 21st and I haven't got this far in the new green book.
 
Last edited by a moderator:
is that regulation a direct quote from new bgb lenny? (dont own one yet, single copy held in boss office for reference)


No, not exactly.

In BS7671, 2008, 131.8 basically stated that no addition or alteration should be carried out unless the earthing & bonding requirements were adequate.

In BS7671, 2011, 131.8 has now become 132.16 and is worded slightly differently.

The guidance I referred to was from the ESC guide on CU upgrades were a TN-C-S earthing system is present.


This is the actual text......


"The minimum main bonding conductor sizes specified in Table 54.8 were first introduced into the Electricity Supply Regulations on 1 October 1988. Smaller minimum sizes were accepted by some electricity distributors prior to that date, but the sizes given in Table 54.8 were introduced to reduce the likelihood of main bonding conductors overheating due to the PME network circulating currents which the conductors may have to carry continuously or for long periods. Distributors may specify larger main bonding conductor sizes where local network conditions require this.


Where a designer finds, in an existing installation where PME conditions apply, that the main bonding conductors have a csa of say 6 mm2 rather than 10 mm2, the designer may, having carefully considered all the circumstances, conclude that the deficiency does not pose a significant risk to the users.

For example, if there is no evidence of overheating of existing main bonding conductors and terminations, it may be reasonable to assume that the existing arrangements are adequate for any network circulating current (unless the main bonding conductors were only recently installed). However, the deficiency must be recorded, together with the reasons why the installer has concluded that the deficiency does not pose a significant risk to the users.

It should be noted that the non-correction of departures from the requirements of BS 7671 is not an option in a new installation or for the rewire of an existing installation".
 
Last edited by a moderator:
You mention 'network circulating currents' in bonding cables. Is there generally current circulating in bonding conductors in PME systems then? I was under the impression that the only time current would flow in bonding conductors would be under fault conditions.
 

Reply to consumer unit change with undersized main bonding. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
811
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

Similar threads

During a new CU installation does the bonding for the gas and water also have to be upgraded to the latest regulations or just tested/ inspected?
Replies
0
Views
208
This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
705

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top