Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer unit was extended at some point:

20230623_111449.jpg


The additional unit is from the kitchen as they had a new kitchen fitted. My concerns are with the quality of the work. No glands are used and all wiring enters the side, the cables also have sheathing cut short so the wires are exposed. I'd have thought some simple chaffing could expose a wire and short the consumer unit:


20230623_111454.jpg


Due to these concerns I opened up the box to take a look at the method used to extend the wires:

20230623_111557.jpg


I have a few questions here... why are glands not used? Is it ok not to use a DIN rail and simply extend all circuits with lever terminals? If so, would splice connectors 221-2411 not be more suitable? If the cables aren't long enough to reach a DIN rail, would it be best to use a Wiska Consumer Unit Relocator for any circuits that do have a wire long enough, and then extend the others?

I'm assuming this is legal, but sloppy work.
 
It's rough but, provided connectors are able to handle the rated current of each outgoing circuit, there's no real issue on that front.

Cables should indeed be restrained and IP rating of enclosures maintained. The main issue, as you've highlighted, is cable sheaths and exposed insulation entering through a cut metal edge. There are a number of ways this could be resolved and glanding individual cables is one of them. To make the best of what you have, I'd probably replace the 2 gang surface box with a small adaptable box and run a short length of 2x2" PVC trunking between it and the board, which would provide space to place some sort of gromment over that cable entry.

I'd be slightly concerned about what's inside your CU, but it may all be fine.
 
Those Wagos are poorly connected, far too much insulation stripped from them. The bottom one appears to have two cpcs in the same sleeve into one terminal. It doesn't bode well for what the consumer unit contains.
 
Cheers all, I like the idea of a Wago XL box - I'll have to check if the original cables are long enough to reach a box as they seem to be quite short.

Here's the CU:

20230624_083432.jpg

20230624_083619.jpg



Seems ok although not the neatest and the grommet looks cross threaded:

20230624_083624.jpg


What was slightly alarming was the lack of sheathing on an earth cable in the side entry:

20230624_083905.jpg



I've put a sheathing on it for now as a temporary measure until its sorted properly. As I unscrewed it, it was pretty chewed up where it joined the earth bar also:

20230624_084122.jpg


I'll look into replacing the surface box based upon how long the cables are...
 

Attachments

  • 20230624_083900.jpg
    20230624_083900.jpg
    477.9 KB · Views: 96
I hate to say it, but looking at that chewed up earth, I fear every terminal was tightened with an impact driver. At an absolute minimum I'd turn the power off and look at the other CPC's (earth wires). If required trim them so you are biting on undamaged copper and loop the end around (similar to how the Neutral's are) so you get a better connection.
 
You would normally put the two lighting circuits on separate RCDs, so one RCD tripping doesn't plunge the whole house into darkness. But it could be done this way because of a borrowed neutral e.g. the landing light (L supplied from downstairs, N to upstairs) and they couldn't be bothered to fix that.
A borrowed neutral is required to be on one circuit rather than just one RCD though for safety reasons (which of course would no longer render it a borrowed neutral).
 
Pretty grim. I've spent time on it today to put new cables in and glands:

20230624_182602~2.jpg



Still not perfect but have addressed the side entry issues. Unfortunately the cables aren't long enough to allow the Wago junction box to be used correctly, what's the best way to resolve this, if any?


20230624_182440.jpg
 
Unfortunately the cables aren't long enough to allow the Wago junction box to be used correctly, what's the best way to resolve this, if any?
Without seeing it for myself this is a bit of a guess, but I'd probably grab a 20mm holesaw and make three or four holes holes is the back of the top of the Wago XL box near the top, mark everything with a Sharpie and then feed the short original wires through the back of the box, resulting in the short wires being nearer the top, and the box being mounted lower down.
When done you should fit cable ties so no one can easily unclip the front.

EDIT you may have to flip 180 degrees so the wago's are at the bottom, and the new cables enter at the top
 
Out of interest, if I ever upgraded to rcbo's, I'm assuming these are all single pole aside from the 'sockets first floor' because I've found this is actually incorrectly labeled and it's actually sockets for both floors with two cables entering the one mcb. Therefore it'd require a double pole rcbo?

...or is it simply wired like that as its a ring and not a radial, therefore still a single pole rcbo
 
Just an observation, but you are aware as a non-spark you're not supposed to be working on a consumer unit ? If something went wrong and traced back to the CU your house insurance company could have an issue with it, let alone buildings control as its notifiable work - Just an observation, I'm surprised no one else has picked up on that in the first post.
 
Just an observation, but you are aware as a non-spark you're not supposed to be working on a consumer unit ? If something went wrong and traced back to the CU your house insurance company could have an issue with it, let alone buildings control as its notifiable work - Just an observation, I'm surprised no one else has picked up on that in the first post.
Looks like he’s more competent than the one that did it originally. 😳
 
I'll be able to sign off domestic installs imminently. Seeing the level of workmanship drove me to study the level 3 etc. The consumer unit is now all sorted and the junction box is completely removed, alls the original installer had to do was move the consumer unit down a foot to make the original wiring long enough 🤷🏻‍♂️

With the removal of the unrequired joins/extensions, and with rcbos and an spd introduced alongside properly 'torqued' connections I'm a lot more comfortable with the installation.
 
Are we going to get into another discussion of what can and cant be done by a homeowner?

If it needs signed off, notified, by a member of CPS... then they wouldn't sell consumer units to joe public in a DIY shed....

Anybody can do the work, then just get a spark to do an EICR on it..... (which would possibly be cheaper to do the work in the first place)
 
Are we going to get into another discussion of what can and cant be done by a homeowner?

If it needs signed off, notified, by a member of CPS... then they wouldn't sell consumer units to joe public in a DIY shed....

Anybody can do the work, then just get a spark to do an EICR on it..... (which would possibly be cheaper to do the work in the first place)
I was commenting on the statement made by muso31- "I'll be able to sign off domestic installs imminently".

As a self confessed non spark, how is this going to work? As the schemes have minimum requirements for joining up, and the only way for a competent person to sign off their own work is by joining a scheme?

Yes, anyone can purchase and install a consumer unit. They may even do the job better than some sparks. And they may produce the correct certification after doing the required testing. And they can arrange to notify building control before commencing the work and pay the fee (usually in the hundreds of pounds). But that's not the same thing as being able to sign off one's own work, including notification to building control.
 
Just an observation, but you are aware as a non-spark you're not supposed to be working on a consumer unit ?
Says who ? He's not replacing the CU, and he's not adding a new circuit. So no notifiable work involved (in England). Of course, the scams would prefer people to think otherwise for the benefit of themselves.
If something went wrong and traced back to the CU your house insurance company could have an issue with it
Possibly, unlikely though.
let alone buildings control as its notifiable work
As noted, not notifiable.
Just an observation, I'm surprised no one else has picked up on that in the first post.
Perhaps because we don't see a problem - other than with the "poor" work that's being put right.
 
Don't see why people can't fit their own, it all depends on how critical you want to be with the paperwork. I may be wrong but its not illegal to not have something like this signed off with a buildings notice, from what I can see it only has to comply with the latest building regulations. So as long as it is fitted according to the latest regs there is nothing anyone can do about it.

There must be thousands of fully built extensions around the country that have never had a completion certificate issued by the local council but they are all still standing, so for half a century or more now without any sort of comeback.
 
It's rough but, provided connectors are able to handle the rated current of each outgoing circuit, there's no real issue on that front.

Cables should indeed be restrained and IP rating of enclosures maintained. The main issue, as you've highlighted, is cable sheaths and exposed insulation entering through a cut metal edge. There are a number of ways this could be resolved and glanding individual cables is one of them. To make the best of what you have, I'd probably replace the 2 gang surface box with a small adaptable box and run a short length of 2x2" PVC trunking between it and the board, which would provide space to place some sort of gromment over that cable entry.

I'd be slightly concerned about what's inside your CU, but it may all be fine.
Rough is being exceedingly generous.

Never ceases to amaze me what people will walk away from.

That could have been so much better with a little forethought, experience and care. Oddly, probably no more cost.

Edi to Add...


Why has the CU been moved 2ft to the right anyway?

It appears to me that they installed a 12way splitty for five circuits.

Probably selling them off at ScrewStation so the fella picked one up, realised it wouldn't fit on the original board and then disappeared down a rabbit hole of poor decisions and workmanship.
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Liverpool
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)

Thread Information

Title
Consumer unit extension wiring
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
30
Unsolved
--

Advert

Thread statistics

Created
muso31,
Last reply from
GBDamo,
Replies
30
Views
7,270

Advert

Back
Top