ChrisElectrical88

-
Mentor
Nearly Esteemed
Arms
Joined
Feb 23, 2013
Messages
2,094
Reaction score
1,681
Location
Wales
Been asked to carry out some works in a bathroom. The clients mains board, cutout and meter are in the airing cupboard of the bathroom currently. As part of the plans they are removing the airing cupboard and plan to just put a standard cupboard with a lock around the mains board which will now be in the bathroom at high level. It will be out of Zones.
I haven’t found out if all circuits are RCD protected yet, I’m also not a fan of it idea but what regs does this go against been out of zone, in a locked cupboard?
 
My one reservation is the locked cupboard, how do you get to the CU cut out in an emergency?
Is there even a requirement to lock it?
The only issue I see is some idiot getting out of the bath or shower soaking wet and going into the cupboard fumbling around.
Would that be likely and should be considered?
 
Is there even a requirement to lock it?
The only issue I see is some idiot getting out of the bath or shower soaking wet and going into the cupboard fumbling around.
Would that be likely and should be considered?

What if someone leaves the door open?
 
What if someone leaves the door open?
Good point!
So this is the process I'm talking about regarding considerations.
Often as electricians we have to wipe people's arses for them, most sensible people would keep that cupboard shut and not entertain going in there. There is also the consideration for children. If the cupboard is accessible by them they may not understand the potential danger.

Good call DPG ?
 

Reply to Consumer Unit in Bathroom in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
512
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
754
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

This was posted this week, on topic ....... https://niceic.com/newsletter/omission-of-overload-protection/?dm_i=7G1W,7GCE,K4L2A,WHET,1
Replies
8
Views
856
Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top