Octopus
FWIW there is NO requirement to upgrade the CU tails to 25mm, especially as you've confirmed the main fuse as 60A
Thanks everyone. Plenty for me to think about which is exactly what I need!
My understanding is any incoming metal service pipework needs to be earthed regardless? Incidentally, just found out my friend was charged for the bonding and meter tails upgrade whatever the requirements are!
Cmin isn't factored into PFC measurements. If anything for PFC you would be concerned about Cmax which isn't even defined.With Amd 3 pfc is calculated as 230 x.95 (Cmin) = 218.5/0.3 = .73 Ka
Better tell the people who wrote GN3.Cmin isn't factored
I don't have my copy on me at present to verify this, but remember this is only a guide book and does not form part of the Wiring Regulations, and indeed may contain errors!Better tell the people who wrote GN3.
Cmax is given a figure of 1.1.Cmin isn't factored into PFC measurements. If anything for PFC you would be concerned about Cmax which isn't even defined.
Where?Cmax is given a figure of 1.1.
Iet 17th edition design guideWhere?
Which comes from IEC documents - my point stands that Cmax is not a defined term within BS7671. (I don't believe even the IEC document refers to it by that name.)Iet 17th edition design guide