NICEIC Certification Scheme Consumer Unit Installation Up to Scratch??? NICEIC approved Installer.

Thanks everyone. Plenty for me to think about which is exactly what I need!

My understanding is any incoming metal service pipework needs to be earthed regardless? Incidentally, just found out my friend was charged for the bonding and meter tails upgrade whatever the requirements are!
 
Thanks everyone. Plenty for me to think about which is exactly what I need!

My understanding is any incoming metal service pipework needs to be earthed regardless? Incidentally, just found out my friend was charged for the bonding and meter tails upgrade whatever the requirements are!


"Bonded"
shinypen,Bonded

He was more than likely stung by a not too rare company which has been badged by the naughty Niceic money grabbers
Maybe the type of courses that enable registration these days promotes standards that are questionable all too often
 
Think there will come a time when you are better off using a contractor not in a scheme.
 
Cmin isn't factored
Better tell the people who wrote GN3.
  • Fault current, I = U0 × Cmin /Zs
where:

U0 is the nominal voltage to Earth,

Cmin is the minimum voltage factor to take account of voltage variations depending on time and place, changing of transformer taps and other considerations.
Pg. 127
 
Last edited by a moderator:
@Risteard If you look in the regs at 411.4.5 411.5.4 etc. and onwards you will see Cmin is factored in to Zs x Ia < Uo x Cmin. Although they dont actually give that formula it is clear in BS7671 it is meant to be factored in by impication. btw I quoted the GN3 verbatim and page number. Although I do agree the Cmax factor may be more appropriate as a safety margin.
 
There is a difference between the prospective fault current and the fault current calculated from the I = U0 × Cmin /Zs formula.
In the second case this formula is being used to determine the trip time of a protective device and so should be the lowest value of fault current that may occur on the installation.
Where you are determining the prospective fault current this is to ensure that the protective device an handle this current so you are determining the maximum expected value that may occur on the installation.
Any protective device must be capable of operating quickly enough at the lowest fault current and also capable of withstanding the highest fault current.
 
Cmin isn't factored into PFC measurements. If anything for PFC you would be concerned about Cmax which isn't even defined.
Cmax is given a figure of 1.1.
Normally used when you want to calc fault current between phases at design stage.
 
Just as a follow up. Had another look today.

The 3 neutrals in to one were actually as follow: 3 x 1.5mm in to one 2.5mm. The mcb was 6amp so not actually dangerous if a little lazy???

There was definitely no bonding in place even though he'd charged for it and recorded it on the cert. Thanks.
 