hello guys
i have a query if you have a C.U. with a 63A main switch fed from a 60Amp main fuse, does the total value of Mcb's fitted have to be below 60Amps before diversity? or is it that as long as the max demand is below the 60Amps ? I have always thought as long as the max demand figure was below the C.U. rating that was ok. just read a note in the OSG about the C.U. having to be able to take total load current applied with no diversity which totally confused me anyone make sense of that ?
i have a query if you have a C.U. with a 63A main switch fed from a 60Amp main fuse, does the total value of Mcb's fitted have to be below 60Amps before diversity? or is it that as long as the max demand is below the 60Amps ? I have always thought as long as the max demand figure was below the C.U. rating that was ok. just read a note in the OSG about the C.U. having to be able to take total load current applied with no diversity which totally confused me anyone make sense of that ?