N

newsparky

Hello can I have some advice please.

I have been asked to move a consumer unit by a family friend.
It needs to be moved 3m which is fine.

The 2 problems that I have -

1. No main protective bonding conductors - which will obviously need sorting before I can change the board.

2. It is a student house and shower cubicles have been put put in all of the bedrooms and there are sockets within 3m of all the cubicles.

The board will need to be changed to a split load dual RCD board as there is no RCD protection for any of it and I will need to carry out a periodic first as there is no previous certification for any of the work (this was originally done 4 years ago).

The main question is can I change the board knowing that there are sockets within 3m of the shower cubicles and code it as a C2 on the periodic or do I have to blank these sockets off before carrying out the board change?
There is no way that the sockets will stay blanked but I need to cover myself.

Many Thanks
 
Sounds like your falling for what lots of people fall for - what if it wasn't a "family friend" ?

Anyone who respects you as a profesional will understand - providing they have it explained to them professionally and they see you as providing solutions.

So it sounds like you've had a look round maybe to price up the EICR so whats wrong with telling them that there are problems that are obvious - the client might not understand but if an electrician installed the showers ? then the possibility of being a latent defect exists ? Suggest they get them back ?

It is a difficult one and i bet if i had a look i'd find other issues too maybe overloading ? and further latent defects ?
I might even consider walking away from this one especially if i didn't have a considerable amount of experience , or at the very least drafting in the help of someone with that experience that you can maybe strike up a reciprocal arrangement with ?

Something you have to learn in this game is nobody knows it all and only a fool thinks they do - we are dealing with lives or the potential for death.

I might be a bit ---- but everything i put in writing is usually ready for court, cover your *rse cos your best mate will sue you if the right buttons are pressed.
 
Sounds like your falling for what lots of people fall for - what if it wasn't a "family friend" ?

Anyone who respects you as a profesional will understand - providing they have it explained to them professionally and they see you as providing solutions.

So it sounds like you've had a look round maybe to price up the EICR so whats wrong with telling them that there are problems that are obvious - the client might not understand but if an electrician installed the showers ? then the possibility of being a latent defect exists ? Suggest they get them back ?

It is a difficult one and i bet if i had a look i'd find other issues too maybe overloading ? and further latent defects ?
I might even consider walking away from this one especially if i didn't have a considerable amount of experience , or at the very least drafting in the help of someone with that experience that you can maybe strike up a reciprocal arrangement with ?

Something you have to learn in this game is nobody knows it all and only a fool thinks they do - we are dealing with lives or the potential for death.

I might be a bit ---- but everything i put in writing is usually ready for court, cover your *rse cos your best mate will sue you if the right buttons are pressed.


well, i've learnt something today. before today i didn't know they spoke english in huddersfield.LOL. :smilielol5:
 
Hello can I have some advice please.

I have been asked to move a consumer unit by a family friend.
It needs to be moved 3m which is fine.

The 2 problems that I have -

1. No main protective bonding conductors - which will obviously need sorting before I can change the board.

2. It is a student house and shower cubicles have been put put in all of the bedrooms and there are sockets within 3m of all the cubicles.

The board will need to be changed to a split load dual RCD board as there is no RCD protection for any of it and I will need to carry out a periodic first as there is no previous certification for any of the work (this was originally done 4 years ago).

The main question is can I change the board knowing that there are sockets within 3m of the shower cubicles and code it as a C2 on the periodic or do I have to blank these sockets off before carrying out the board change?
There is no way that the sockets will stay blanked but I need to cover myself.

Many Thanks
aand so you will have done as well....what the client/tennent does afterwards is their problem....if they tamper with it...
 

Reply to Consumer Unit Move in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

If two tariffs are sufficient, and you don't need too many ways, you can easily add an SPD kit to the Fusebox F2014DT dual tariff board. The only...
Replies
1
Views
287

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top