I changed this to a single CU as well thought it best..Customer kept getting electric shocks as well...before not after!
there is a good video thats just popped up on my youtube feed, from that bloke john ward. it covers EICR's and will give you lots of ideas, havent watched it all (its an hour long) but given a lot of his videos are quite informative might be worth a watch and help you understand various points
Can anyone give me a list of things from an EICR that might mean that your consumer unit might need replacing
? is this a serious question? if so please come back and explain why you asked this and maybe we can try to assist you, that said, I am concerned you are in one of two camps. 1, you want to justify replacing a DB, or 2, you have been told yours needs replacing and you are not sure.
I tend to agree with the above posts, however I think I remember that you are early on in your career, so may be attempting to learn, the assessment for a CU change is more than an EICR result and to not realise this indicates a lack of awareness.
However I did go through the EICR observations for distribution boards and came up with the following, if the observation was coded for danger would the consumer unit need changing?
Consumer Unit(s) / Distribution boards
Equipment Working space / accessibility adequacy(132.1.2,513.1)- No, but perhaps moving
Security of fixing (134.1.1) – No, repair
IP rating of enclosure suitability (416.2) – possibly, possibly repair
Fire rating of enclosure suitability (526.5) ) – possibly
Enclosure not unsafely damaged (621.2(iii)) ) – possibly, possibly repair
Main linked switch present (537.14) ) – No
Main switch operation (612.13.2) ) – No, repair
Disconnection of circuit breakers / RCDs proved (612.13.2) ) – No, unless replacement PDs no longer available
Protective devices correctly labelled & identified (514.8,514.9.1) ) – No, repair
RCD quarterly test notice present locally (514.12.2) ) – No
Mixed cable colour warning notice present locally (514.14) – No
Alternative supply warning notice present locally (514.15) – No
Other required labeling present (specify) (S.514) – No
Protective Devices & bases of correct type & rating, no signs of thermal damage or arcing (421.1.3) – possibly
Single pole protective devices in line conductor only (132.14.1,530.3.2) – No, repair
Cable entries protected against mechanical damage (522.8.1,522.8.11) – No, repair
Cable entries protected against Electromagnetic effects (521.5.1) – No, repair
RCD/RCBO(s) provided for fault protection (411.4.9,411.5.2,531.2) No, unless PDs no longer available
RCD/RCBO(s) provided for additional protection (411.3.3,415.1) No, unless PDs no longer available
SPD device(s) functional (if present) – No
Confirmation that all connections correct and firm to terminals / busbars– No, repair
London
Consumer unit replacement
Bradley6969,
Richard Burns,
