pablod

hi,

when changing over a consumer unit is it correct practice to test R1 and R2 on all fittings on all circuits or is it acceptable to test on the point furthest on each circuit.

one other point. am i correct in saying on the light it is ok on the IR test (at 500v) to connect line and neutral together to earth. half the house is low voltage lighting and testing this way means i wont have to dissconnect the transformers?.

thanks for ya help in advance. im newley qualified and have a consumer unit chane next week for me assessment.
 
Short answer yes and yes. When changing a consumer unit you're under no obligation to test the installation, however it's best practice to carry out a periodic inspection so just make a note of your limitations in testing.
 
The alteration or addition itself (the installation of
the replacement consumer unit and any other new
work, such as additional final circuits) should be
verified fully in accordance with the requirements of
Section 610 of BS 7671 and an Electrical
Installation Certificate in accordance with BS 7671,
detailing the work, should be given by the installer to
the customer.
10.2. In addition, as a minimum, the following tests
should be carried out to the existing circuits
connected to the replacement consumer unit.

• A continuity test of the protective conductor of
each circuit, to the point or accessory electrically
furthest from the consumer unit and to each
accessible exposed-conductive-part.
• A continuity test of all ring final circuit
conductors.
• A measurement of the combined insulation
resistance of all the circuits. The measurement
need only be made between the line and neutral
conductors connected together and the
protective conductor connected to the earthing
arrangement.
• A test of the polarity and a test to establish the
earth fault loop impedance (Zs
), at each
accessible socket-outlet and at least one point or
accessory in every other circuit, preferably the
point or accessory electrically furthest from the
consumer unit.
Note: Testing of each RCD using both a test instrument




The above is copied and pasted from here, its worth reading
http://109.75.163.57/fileadmin/user_upload/documents/industry/best_practice/BPG6_09.pdf
 
Last edited:
cheers for that guys one thing i just want to check on. when IR testing at 500v and combining line and neutral it is ok to leave transformers and all ights connected. i dont want to be doing any damage as this would be the first time im doing the line and neutral together as i have done all my testing the standard way.

cheers
 
When doing a cu change I like to R1 + R2 at all points on all circuits as even if you have continuity at the most remote point of a circuit it does not mean you will at all other upstream points.
If all is well you should get the highest reading from the most remote point on that circuit which will be recoreded as R1+R2 for that circuit but this is not always the case.
When doing IR test you could use a shorting lead at the cu on the live and neutral and test between live/neutral and earth, But you must remember to remove the link before re-energising the supply.
 
hi and thanks cjp1,

the way i was shown when training was to connect line and neutral in a block and leave the cpc in the earth bar. just checking this is the same. i beleive it is.

paul
 
hi and thanks cjp1,

the way i was shown when training was to connect line and neutral in a block and leave the cpc in the earth bar. just checking this is the same. i beleive it is.

paul

Hi Paul, I am not quite sure what you mean about connecting the line and neutral in a block?
you could make a tempory connection between line and cpc using a connector block at the consumer unit when doing you R1+R2 for a radial circuit.
cheers chris
 
Be careful that you are sure and safe
I find the easiest of all methods is to switch off the supply,engage all mcbs and link with a wire with crocodile clips from the bus bar/s to the neutral bar/s and test between the bus bar or neutral bar and the earth terminal
 
If you are testing the whole installation then do not use a connector block, as you would need to connect every line and every neutral into the block. The connector block would only be used for testing a single circuit. However it is easier to just link them as mentioned above.
A 500V test should not damage anything but check at 250V first and if you get a low reading check for delicate items in circuit. ELV light transformers and dimmer switches should ​ be OK.
 
cheers for that guys one thing i just want to check on. when IR testing at 500v and combining line and neutral it is ok to leave transformers and all ights connected. i dont want to be doing any damage as this would be the first time im doing the line and neutral together as i have done all my testing the standard way.

cheers


When you connect the line and neutral at the board , you take away the possibility of high current ( due to 500v going down it) going through the tx / lights/ aplliances ....since current will only flow from 230v - 0v....or 200 - 50 ..../ any place with a difference between the voltage ( ie potential difference )

Connecting live and neutral means you put 500v on the l+n at the same time. so no currents.

Hope this helps and im correct. LOL
 

Reply to consumer unit testing question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
864

Similar threads

I have ascertained that I can have a fuse wire type consumer unit provided it passes the EICR tests and also that it can be in a waterproof...
Replies
2
Views
738
  • Question
I have to agree with Baldelectrician on almost everything he says except one ! I wouldn’t be walking away I’d be running lol. Definitely if your...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top