pablod
hi,
when changing over a consumer unit is it correct practice to test R1 and R2 on all fittings on all circuits or is it acceptable to test on the point furthest on each circuit.
one other point. am i correct in saying on the light it is ok on the IR test (at 500v) to connect line and neutral together to earth. half the house is low voltage lighting and testing this way means i wont have to dissconnect the transformers?.
thanks for ya help in advance. im newley qualified and have a consumer unit chane next week for me assessment.