Consumer Unit | Page 2 | on ElectriciansForums
Discuss Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net
Consumer unit change was done on Domestic dwelling.
New consumer unit was a split load x2 RCDs.
After installation, inspection and Tests, one of the RCDs trips whenever I load the other RCD. I mean if I put a load say plug in an appliance on a socket the other RCD, or switch the oven on, the other RCD trips even though the appliance plugged in this RCD is still working.
I have checked to be sure there are no crossed neutrals. But it still keeps tripping
What comment do you have please???
Regards.
rite:
its a neutral earth fault...coming back through the PME block....
drop the neutrals out and test to earth...find the offending circuit...then divide & rule on the circuit (split it roughly in half)...this way you can negate half straight away....saves time see....
hi glenn, would this kind of described fault be more likely found on circuit protected by rcd that trips or one that doesn't?
Think I might take a look at the lighting circuits for starters.
Have you tried switching 'em on?....same result?
sounds like a shared neutral on the lights , to check for this put all lighting circuits on one side , covered by one RCD if it all holds , then you will need to now go and find where they are shared , one common situation is the landing and hall lighting sharing neutrals , but it could be many places , I would try this with the lights first though..
Reply to Consumer Unit in the UK Electrical Forum area at ElectriciansForums.net