Consumer unit change was done on Domestic dwelling.
New consumer unit was a split load x2 RCDs.
After installation, inspection and Tests, one of the RCDs trips whenever I load the other RCD. I mean if I put a load say plug in an appliance on a socket the other RCD, or switch the oven on, the other RCD trips even though the appliance plugged in this RCD is still working.
I have checked to be sure there are no crossed neutrals. But it still keeps tripping
What comment do you have please???
Regards.
sounds like a shared neutral on the lights , to check for this put all lighting circuits on one side , covered by one RCD if it all holds , then you will need to now go and find where they are shared , one common situation is the landing and hall lighting sharing neutrals , but it could be many places , I would try this with the lights first though..
One other thing you have to take into account , is when you did the testing if the light switches were in the off position then the fault would not show up when doing IR or continuity tests at the board