O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz )
Thank you for all the easy to read info... you made it easy to follow, thank you
Calculationof Earth Fault Loop Impedance :speechless:
The most commonly used measure . Automatic Disconnectionof supply either the Overcurrent protective devices - Which also provideprotection against “ Overload &Short circuit Currents for the circuit Concerned .
ResidualCurrent Devices . RCDs or combined devices RCBOs . Whichever type of device ischosen .
TheEarth Loop Impedance that has to be considered is that which comprises the Impedance of the Source .
TheLine conductor up to the Fault plus the Protective Conductor from the fault to the Source .
Whys& How’s .
Note:- That when an RCD or RCBO is used to provide Automatic Disconnection of thesupply in a ( TN- system ) the calculation of ( Zs ) is normally “ Unnecessary “ provided that “ Continuity“ of the EarthLoop has been Established . ◄◄
Anotherreason for calculating the Earth Loop Impedance is to check that the “ Circuit Protective conductors are adequatelyprotected thermally . & That they comply with the “ Adiabatic Equation givenin Regulation . 543.1.3. – Subject ofChapter 4 .
BS-7671:2008– Bottom of . Table 41.3 – NOTE.
ContainsNO requirements in relation to the Conductor Temperatureat which the Earth Loop Impedance iscalculated .
Note :- The notes to the tables of Maximum Earth FaultLoop Impedance . – Table 41.2. – to 41.4. . States . that the Tabulated Valuesshould NOT be exceeded when the conductors’ are at their Normal Operating Temperature.
ifthe conductors’ are at a different temperature when tested . The reading should be Adjusted Accordingly – Appendix 14.
Current – Carrying Capacity . ofa Conductor . :speechless:
TheMaximum Current which can be carried by aconductor under Specified Conditions without itssteady state temperature exceeding a specified value.
Apprentices.
Namethree types of “ Diagram “used in the Electrical Industry . & explain – ThereUse . :icon_bs:
Anythree from Wiring diagram . Circuit diagram . Block diagram . Layout drawing .Installation drawing . Schematic drawing . Site plan .
A wiringdiagram provides a pictorial representation of an Electrical Circuit . showing arepresentation of the components .
A blockdiagram typically shows the flow of aprocess . each function being represented by a block .
A schematicdiagram uses symbols to show the arrangement of a system clearly .
Whereasa layout diagram shows the physical arrangement of the wires & components .
:45:2392-10: ▼
Q) The main switch in a “ Single – Phase “ domestic Installation interrupt’s how many “ Live Conductors “
-&-s: BS-7671 – Regulation 537.1.4. The main switch should interrupt both LiveConductors on a Single/Phase Supply .
A MainSwitch intended for operation by “ Ordinary Person“ of a Household or similar Installation . shall Interruptboth Live Conductors of a Single-phase supply .
Q) How many poles would the main switch on aThree-phase & Neutral – TN-S supply have .
Threepoles - BS-7671 – Regulation 537.1.2. The Neutral neednot be Switched . ( TN-S or TN-C-S )
2392-10: ▼
Q) State: Two precautions that must be takenbefore carrying out Insulation Résistance Testing .
i) Remove sensitive equipment – Dimmers .Programmers . P.I.R.
ii) Remove equipment that “ GIVES “ falsereadings – Lamps . Neon’s . Motors .
iii)Check it is Safe to continue with the Test . When applying – 250 / 500V .
-&-s: Make sureNo-one else is in contact with any part of the Circuit .
2392-10: ▼
Inrelation to Electrical Installations . :waving:
Whatis meant by Maximum Demand :- This is an Assessment of the current demand of an Installation.
Whatis meant by Discrimination :- The co-ordination ofprotective device(s) so that the device nearest to the load . being of a lowerrating . operates before the device futher up the line . Thereby minimisingloss of supply when a fault occurs .
Whatis meant by Diversity :- An allowance given when calculating maximum demand . due tothe fact that not all of the appliances . will be Used at the Same Time .
2392-10:
FunctionalTesting ?? :waving:
Testing of Switches . Disconnections. Controls . RCDs . to check that they FunctionCorrectly .
2392-10:
ApprovedVoltage Tester . To - GN-38 . :waving:
State:- Three of the requirements for Test Leads .
i) Retractable tips . or not more than ( 4mm) prefer 2mm . Fingers guards . Robustleads . coloured or identified . long enough for the purpose . Fused probes .
State:- the method of Ensuring it is working Effectively .
ii) By the use of an Approved Proving Unit .Testing the voltage tester . Before & After testing the equipment . or Circuit .
Definitions’/ p/23 . EarthingConductor
A protectiveconductor connecting the main Earthing Terminal of an Installation to an EarthElectrode or to other means of Earthing .
Connectsthe main Earthing Terminal to the source of Earth . either an Electrode ( TT ) or means ( TN-S or TN-C-S ) :95:
2392-10: ( T )
Howis Discrimination achieved when Using RCDs . :- Byusing Time-delayed RCDs . :79:
Insight to the working of 17[SUP]TH[/SUP] Edition . “ Examples “
BS-7671:2008. Section 708 – Caravan & Camping Parks .
Thisis accommodated by the provision of suitably placed socket outlets . supplied via distribution circuits .
External Influences .
Equipmentshould have at least the following protection codes .
Impactrésistance . 708.512.2.
IPX4– for the presence of Splashes – ( AD4 ) in accordance with BS-EN 60529.
IP3X– for presence of small objects - ( AE2 ) in accordance with BS-EN 60529.
IK08- for presence of high severity mechanical stress ( AG3) in accordance with BS-EN 62262 .
(The ( IK ) codes are for Impact & ( 0.8 ) is an Impact of ( 5-Joules ) ImpactRésistance .
( Environment – p/324 . AG3 – High Severity . Reinforced Protection . IK08 )
British Standards to whichReference is made in the Regulations . Appendix1 – “ Normative “ p/228 – ( Requirement )
BS-EN 62262:1992 . – 2004 . Specification for degrees’ ofprotection provided by enclosures ( IP Code )
527.2.6.– (i) the system satisfies the test of BS-EN 62262 for ( IP33 )
527.2.6.– (ii) any termination of the system in one of the compartments , separated bythe building construction being penetrated . satisfies the test of BS-EN 62262for ( IP33 )
702.512.2.: External Influences . Electrical equipment shall have at least the following degree of protection according to BS-EN 62262. ( IP ???? )
708.512.2.- (i) & (ii)
708.553.1.8.each socket-outlet & its enclosure forming part of a caravan pitch electricalsupply equipment shall comply with ( BS-EN 60309-2 ) & meet the degree of protection of at least( IP44 ) accordance with BS-EN 60529 .
A721.55.6.- p/218. Terminal blocks .
A721.55.10.- p/218. External lights .
Note : Section 721 : tells us . p/209 – Wording . Yeah :96:
Inorder not to ►► MIX ◄◄ Regulationson different Subjects such as those for Electrical Installation ofcaravan parks with those for Electrical InstallationINSIDE caravans .
Section– 708 . concerns Electrical Installations ( IN ) caravanparks . camping parks & similar locations & . Outside.
Section– 721 . concerns Electrical Installations ( IN ) caravans& motor caravans . Inside
WiringSystems .
Thedistribution circuits are erected either Underground or Overhead .
708.521.1.1.- i) Underground cable ( Preferred )should be suitably protected against Mechanical damage . tent pegs . steelspikes . & at a depth of NO less than ( 0.6m )
708.521.1.2.- ii) Overhead . if overhead . Then ( 6m) above ground where there is Vehicle movement ( 3.5m ) elsewhere .
Switchgear& Socket outlets .
708.530.3.- Supply equipment should be adjacent to . or within ( 20m ) of the pitch .
708.553.1.8.– Socket-outlets should be :- BS-EN 60309-2– ( IP44 )
708.553.1.9.- at between ( 0.5m to 1.5m ) aboveground .
708.553.1.10.- rated not less than ( 16A )
708.553.1.13.– each socket-outlet shall be protected individual by an ( 30mA ) RCD protection. ( The device shall disconnect all LIVE CONDUCTORS including the NEUTRAL.
708.553.1.14.– if the supply is ( TN-C-S ) the protective conductor of each socket-outletneeds to be connected to an ( Earth Rod ) Regulation – 411.5. TT System .
AdditionalProtection . :hurray:
703.411.3.3.Sauna heater .
Allcircuits in the location should have “ Additional Protection “ against shock by30mA RCD .
Except Sauna heater circuits unless Recommended by the Manufacturer . :svengo:
External :- Earth Fault Impedance . ( Ze )
The Importance of this Test . To establish that a good Earthexists at the installation in order for the Remainingtests to go ahead . :svengo:
Additions & Alterations to anInstallation . :waving:
General :
Many existing electrical installations require one or moreAdditions or Alterations during their lifetime . An Addition or Alteration maybe minor ( such as the Addition of a point to a final circuit . or therepositioning of a point ) or major ( such as the Addition of a new finalcircuits . distribution circuits . distribution boards & an upgrade to thesupply .
Where an Addition or Alteration ( which temporary or permanent) is to be made to an installation . the relevant requirements of BS-7671 .have to be met such that both the Addition or Alteration is Safe . & thesafety of the Existing Installation is not Impaired.
In order to be meet the requirements of BS-7671 . Followingmust be undertaken .
• Assessment ofthe existing installation to establish that the parts upon which the Additionor Alteration will rely for safety are both present & suitable for thealtered circumstances . & will continue to be so . & that the supply issuitable .
• Upgrading of parts of the existing installation . where foundnecessary to safely accommodate the Addition or Alteration . as a result of theabove Assessment .
The electricity distributor will need to upgrade thesupply . if Necessary .
• Design & construction of the Addition or Alteration inaccordance with the requirements of BS-7671 .
(T) • Inspection &Testing of any upgrading of the existing installation . & of the Addition or Alteration . as requiredby chapter 63 of BS-7671:2008
• Certification of any upgrading of the existing installation . & of the Addition or Alteration . as requiredby chapter 63 of BS-7671:2008
Assessment of an Existing Installation .
Regulation ( 131.8.) requires an Assessmentto be made of the relevant parts of an existing installation which is tobe Added to or Altered of the Supply .
Regulation ( 131.8.) No Addition orAlteration . temporaryor permanent shall be made to an existing installation . unless it has been ascertained thatthe rating & the condition of any existing equipment . including that ofthe distributor . will be Adequate for the Altered circumstances . furthermore . The Earthing & Bonding arrangements . if necessary for theprotective measured applied for the safety of the Addition or Alteration . shall beAdequate .
Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...