amberleaf

O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 Ă· 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Purposeof . Periodic Inspection & Testing . 621.2. is to provide an Engineering view . on whether or not theinstallation is in a satisfactory condition where it can continue to be usedSafety .

Itshould be noted that the initial . sample size is only based on a . walk-round .& consultation of . records . further . that what may at first appear to begood . E.g. the quality of maintenance . may turn out to be poor during the detailed inspection & testing .

Suggestedprocedure for setting . Initial & adjusted sample size .

Conductinitial “ Walk round “ survey &establish initial sample size .
â–Ľ
Carryout Inspection & Testing . based on initial sample size .

â–Ľ Good results .
Goto final report .

â–Ľ Intermediate/ poor results .
Increasesample size . or discuss with Client . whether further investigation is required .
 
Stillthe same . 2391-10 :

Low-résistanceohmmeters . BS-EN-61557-4 .
(IR ) testers . BS-EN-61557-2 .

Earthfault loop impedance testers . BS-EN-61557-3 .
Thismeans that the instrument should cut OFF the test current after [ 40mS ] Etc .

(RCD ) testers . BS-EN-61557-6 .
Reminder . 2392-10 . -&-s
Tocheck RCD . operation & to minimise danger during the “ Test “ the test current should be appliedfor no longer than [ 2s ]

Phaserotation instruments . BS-EN-61557-7 .
Exams: Mechanical . visual & / or audiblemeans .
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 
I'm just bumping some threads in the Electrical Forum, don't mind me while I do this, you don't have to respond to them. Although if they are still current topics, and you do wish to reply, you're welcome to. Keep the thread on-topic and make sure you stick to the forum rules though.
 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
273
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
777

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top