A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
Are any changes beingmade to the 2392 Fundamental inspection, testing and initial verificationqualification ?
The2392 qualification will be migrating to the QCF in late 2011, with very few changes tocontent or the assessments. More details will be released in autumn 2011.
2392-10:
Protectionagainst Sock .
Provethat the following tables provides ( Instantaneous Disconnection ) for a . BS-EN-type 32A. MCB using tables ( 41.3. – App 3 )
Conformsto :
( Zs ≤ Uo / Ia )
17[SUP]th[/SUP] Edition 2008:2011 )- Table – 41.3. End of the Table . !! ( Type B . 46/In ) ( Type C . 23/In ) ( Type D . 11.5/In )
Zs ≤ 230 ÷160 = 1.44Ω .
( Type B . 46/In ) ► 46 ÷ 32 = 1.44Ω . Maximum ( Zs ) table 41.2
230÷ 46 = 5 . In . multiplier for instdist .
Min. Amps . for inst . dist (Appendix 3 )
Manufacturesdata show ( 3 – 5 * In ) for instantaneous disconnection .
B. > 3 In . ≤ 5.0 In
C > 5In . ≤ 10.0 In
D > 10 In . ≤ 20.0 In
Protection Against Electric Shock .
Protectionprovided by s Residual Current Device ( TN- systems )
Followingcondition applies . Regulation – 411.5.2.
( Zs x IΔn ≤ 50V )
• ( Zs ) = Earth Fault Loop Impedance in Ohms . Ian= rated residual operating current in Amps .
Protectionin ( TT system )
Theuse of Overcurrent Protective Devices are NOTexcluded . although it is preferred to use a ( RCD) with a disconnection time of NOT greater than ( 1 sec ) 411.3.2.4.
R[SUP]A[/SUP] x Ia ≤ 50V .
Regulation– 411.5.3.
R[SUP]A[/SUP] = sum of all the resistances of earth electrode& protective conductors connected to the Exposed – conductive – parts .
I[SUP]A[/SUP] = the current causing automatic operation of theprotective device with ( 1 sec )
Allowancesfrom Table 41.1. :
411.3.2.3.– TN - systems disconnection time < 5 sec for a . distribution circuits .
411.3.2.4.– TT - systems disconnection time < 1 sec for a . distribution circuits .
Not covered by . 4113.2.2. – ( > 32A circuits )
411.3.2.6.– where disconnection times cannot be met then ( Supplementary Bonding ) must beApplied .
In some Applications where the continuity of service is very high .
“ Hospital “ Operating Rooms . as we can’t accept the tripping of Electricity oncean Earth Fault Occurs .
- Areswhere the Explosions risk is High .
• Omission of Protective devices for SafetyReasons . 2008:2011.
433.3.3. .
Used where unexpected disconnection would cause a dangeroussituation .
i) the exciter circuit of a rotating machine .
ii) the supply circuit of a lifting magnet .
iii) the secondary circuit of a currenttransformer .
iv) a circuit supplying a fire extinguishingdevice .
v) a circuit supplying a safety circuit (fire or gas alarm )
vi) a circuit supplying Medical Equipment used for Life – support in specific Medical Locations’ . where an ( IT ) systems . is incorporated .
aswe know . there are Three- Types ofEarthing Systems in the 2011 .
TN-S.
TN-C-S – ( PME ) .
TT.
Fora ( Low-voltage ) supply given in accordance with the .Electricity Safety . Quality & Continuity Regulations . 2002 .
Deleted by BS-7671:2008 – Amendment . No 1 .
IT) & ( PEN ) is withdrawn .
i) - This is because ( TN-C ) requires an ( Exemption ) from the . Electricity Safety . Quality &Continuity Regulations .
ii) - & ( IT ) system is NOT permitted for a ( Low-voltage ) public supply in the UK. Because thesource is NOT directly Earthed .
(1 ) I split this Question up . of the Net.
Whichone of the following ( Test Readings ) for Continuity of CPC. Would satisfy BS-7671:2011 for a 230V A.C.lighting circuit . ( 0.5Ω )
10MΩ.
100Ω .
1MΩ.
0.5Ω
Calculations’: 230V ÷ 0.5Ω = 460A .
460A )- this is Fault Current would easily disconnect the 6A – MCB .protective device within 0.4 seconds (TN- Earthing system ) Why??
p/301– fig . 3A4 . Type B– BS-EN 60898 .
MCB . BS-EN – 60898 .
Rating– ( 6A ) . Current - ( 30A )
RCBO is / MCB / RCD
Overcurrent characteristics of RCBO to BS-EN- 61009-1 : MagneticSettings )- 5 x 6A = 30A . ( Zs < 230 ÷ 30A = 7.67Ω ) table – 41.3 - 6A / 7.67ohms )
( 32A )- RCBO toBS-EN- 61009-1 : Domestic Installation. MagneticSettings )- 5 x 32A = 160A. ( Zs < 230 ÷ 160 = 1.4375 – 1.43. table – 41.3 - 32A / 1.44ohms )
(Zs ≤ 230 / 160 = Zs ≤ 1.43Ω )
-&-s. The maximum ( Zs ) for a BS-EN-60898 . 32A . B type circuit breaker protecting a DomesticRing Final Circuit is . table – 41.3. 1.44Ω .
Witha Spilt –Load . Consumer Unit .
Regulation314. (i) Splitthe Circuit(s)
Downstairslights are on the same RCD as the Upstairs sockets . “ Reason “ forthis is that . if the RCD trips & Downstairs lights go OFF . Downstairs’ sockets are ( Still Live ) the User can plug a tablelamp into One of Them .
Regulations522.6.102. p/125 .
Meansthat such ( Additional RCD Protection ) applies alsoto Lighting circuit(s) . to eliminate the risk of both Lighting circuit(s) . going OFF simultaneously because OFF nuisance tripping .
Each“ Lighting circuit on a Separate RCD.
BathroomLighting Circuit . ( Supplementary equipotential Bonding ) may be Omitted within a Bathroom or Shower .where the conditions of Regulation 701.415.2.are Complied with .
Theseconditions include the requirement that all ( Final circuit(s)within the location have ( Additional protection ) by means of a 30mARCD
TheBathroom Lighting Circuit is supplied by means of a Separate Circuit.
Where Regulation 522.6.101. applies& the installation is NOT intended to be UNDER the supervision of a ( Skilled or Instructedperson ) a cable installed in accordance withRegulation 522.6.101 – (v) & NOT also complying with Regulation . 522.6.101– (i) . ( ii ) . ( iii ) . or ( iv )
Shall be provided with ( Additional protection ) by means of an ( RCD ) having the characteristics specified inRegulation 415.1.1.
522.6.101 . p/124 .
(iv)– be mechanically protected against damage sufficient to prevent penetration ofthe cable by Nails . Screws & the Likes .
531.5. RCDs in an ( IT )
Whereprotection is provided by an RCD & disconnection following a ( First Fault ) is not envisaged . the Non-operating .residual current of the device shall be at least Equal to the current whichcirculates on the ( First Fault ) toEarth of negligible impedance affecting a Line Conductor .
Socketoutlets . 411.3.3. p/54 .
(i) All socket outlets for general use byOrdinary persons Not Exceeding ( 20A ) .should be protected by a . 30mA – RCD .
Plain English )- p/31. Ordinary Person . A person who is neither a skilled person nor an instructedperson .
TheWording is that socket – outlets with a rated current NotExceed 20A . that are for use by ( Ordinary Persons) & are intended for general use areto be protected .
2392-10. Intended to cover all who dwell in . Houses . Flats . Yeah .
PortableEquipment . see ( Mobile ) p/31 .
(ii) All ( Mobile ) equipment foruse Outdoors should be protected by a . 30mA – RCD . Notexceeding 32A . for use Outdoors .
Mobile equipment ( Portable equipment –( deprecated )) .Electrical equipment which is ( Moved ) while in ( Operation ) or which caneasily be moved from one place to another( while Connectedto the Supply )
SpecialLocations .
Allcircuits in a room with fixed bath or shower should be protected by one or more. 30mA – RCD . shower . lighting . Heater . Ventilation .
( T ) Fundament Principles . 132.13. ( Documents for Electrical Installation(s)
514.9.1. & Part 6. - & whereapplicable . Part 7 . is provided for everyElectrical Installation .
Regulation. 134.1.1. Erection & Initial Verification of ElectricalInstallation(s) requires that goodworkmanship shall be undertaken by ( Competent Person(s) & further requires ( ManufacturesInstruments ) shall be followed .
2392-10: if we reposition a ( Pull cord ) switch in a location containing abath or shower . Would the circuit need to be RCD protected . YES .
Yesbecause the work would be more than a ( Likeforlike - replacement ) Regulation . 701.411.3.3. .
2392-10.
• Fundamental Principles . ( Scope ) p/14.
(vi ) additions &alterations to installations & also parts of the existing installationaffected by an addition & alteration .
Amendment No 1 . 2011 .
16[SUP]th[/SUP] Edition - Which has renamed Periodic Inspection Reports- ( PIRs ) TO.
ElectricalInstallation Condition Reports – ( EICRs )
UsefulJunk .
Underthe existing arrangements . 2011 . the codes will have a Letter “ C “ for code . in front of them .
2392-10: These reports are also used by placesof work to demonstrate ( Compliance ) with the Electricity at Work Regulations 1989 .
Thetypes of properties that typically fall within the ( EICRs ) guidelines .
BS-7671:2011. Scope . p/14 .
2392-10.
110.1.1. . The regulationsapply to the design . erection & “ Verification “ of electricalinstallations such as those of : E.g.
i)residential premises .
ii)commercial premises .
iv)industrial premises .
vi)prefabricated buildings .
xv) medical locations .
p/36. ( T ) “ Verificationall measures bymeans of which compliance of the electrical installation with the relevant requirementsof BS-7671:2011 . are checked . comprising . Inspection & Testing &Certification .
ElectricalInstallation Condition Report . ( EICR )
PeriodicInspection is an Inspection on the condition of an ExistingElectrical Installation . To . Prioritiseany deficiencies against BS-7671:2011
Oneway of confirming an ( Existing Electrical Installation ) is safe forcontinued use to have the Installation ( Periodically Inspected & Tested ) & a“ Report “ on the Condition ( Issuedto the personOrdering the Work )
Mustmake this clear . 2392-10 : -&-s . TRIP UP ONE
Electrical Installation Condition Report “ is asthe title indicates a “ ReportNOT a CERTIFICATE . ◄◄ -&-s
Itrelates to an assessment of the . “ in service condition “ of an Electrical Installation . against therequirements of the Current Edition of BS-7671-2011
-&-s )- the “ Report “ is primarilyfor the benefit of the person ordering the Work .
“ Wording . “ 2391-10Exams
Electrical Installation Condition Report Certificate . N/A - NO MARKS :banghead:
Electrical Installation Condition Report .
( Periodic Inspection & Testing) of an Electrical Installation is also ( recommended ) atthe end of the ( Period stated ) on the ( ElectricalInstallation Certificate ) Or .the Last ( ElectricalInstallation Condition Report )
Q/As . -&-s .
An ElectricalInstallation Condition Report . shouldinclude details of the ( Extent of the Installation) &
Any( Limitations of the Inspection & Testing )
The( Reasons for any such Limitations )
The ( Main purpose) of having your Electrical Installation checked is therefore to ( Identify ) so far as is reasonably practicable . & ( Report ) on any factors Impairing or likely to impair the safety of the Electrical Installation .
Visual Condition Report :
Thisreport is intended to be issued only for the purpose of reporting on conditionof an “ Existing Electrical Installation
Ingeneral a ( VisualCondition Report ) is suitableonly where the Installation has been Inspected & Tested within the last twoyears & the results were reported on an ElectricalInstallation Certificate . Or an Electrical Installation Condition Report .
Note . that a “ Visual ConditionReport “ includes ONLYthe findings of the Inspection of an Electrical Installation .
Note . it does NOTinclude the results of any Electrical Testing.
-&-s: just because I’m paranoid doesn’t meanthey’re not out to get ME .
Visual ConditionReport “ isreally a “ Electrical Installation Condition Report “ without the Measurement(s) . :13: Yeah .
***Cont../ Useful Information for Electricians & Apprentices***
Australia
amberleaf,
Dan,
TrueNAS JBOD Storage Server