Contactor control circuit | on ElectriciansForums
Discuss Contactor control circuit in the UK Electrical Forum area at ElectriciansForums.net
Kings Lynn
Hi guys and gals, I am struggling to figure out how to achieve what seems to be a simple control circuit. I’ve wired a test rig and the system works as expected apart from the lamp not illuminating! What I am trying to achieve is a 13amp socket controlled contactor. Part of the control circuit will be a 230v 15watt warning lamp, once the lamp blows or is removed the contactor will drop thus de-energising the 13amp socket. When tested the lamp glows ever so slightly so obviously there’s an issue with such a high resistance of the contactor coil! Is there a different type of coil available on the market with a lower resistance? Is there another method that I’m not thinking of? Advice would be much appreciated. Thanks in advance.
You have lamp and contactor coil in series.....you have a dim lamp......what do you think is happening! :)
@Andy-1960 beat me to the punch, I'd be using a current sensing relay. Have its control contacts cut the contactor if your indicator lamp burns out.
If you need to run a lamp in series with the coil, you'll need to very carefully balance the current & voltage ratings to give reliable operation, a non-trivial challenge without detailed specs.
Yes buddy this would be as close as I have got so far.
These machines are used by trained professionals. We’re are simply talking about a power supply, a contactor and a warning light. Once energised these mobile machines have to be activated by competent persons.
I think the point we're trying to make is... if this warning light is the only thing standing between a non-competent person getting an unwanted dose of x-rays and them not, then it needs to be pretty bullet proof in terms of reliability.
I'd be thinking multiple lamps, possibly two sense relays and two contactors to provide some level of fail safe setup.
There are special relays I believe that are designed for use in safety solutions that basically prevent operation if a component fails, but machine safety is a specialised area that I'm not familiar with.
Out of interest, what specific regulation are you trying to comply with here?
Off the bat there would seem to be a few cheap solutions as oppose to building a monitoring circuit, an example been redundancy, why not just have 2 lamps and when one fails it is clearly obvious and maintenance will repair it or the user trained to report it.
That aside the current monitoring option seems the best as previously mentioned but my concern is your reliance on a contactor to isolate a power outlet, if this is for safety then by design it needs to be fail safe and have redundancy in the design thus the contactor needs monitoring as well via a safety control circuit... when you are trying to comply to machine code standards or similar standards then what often seems a simple solution can require a expensive and complex system to ensure safe use and operation.
Reply to Contactor control circuit in the UK Electrical Forum area at ElectriciansForums.net
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...