B

bennjy

Hi
I've installed the electrics for an underfloor heating system. The system has 6 manifolds each with a small pump. There is then a primary pump that pushes hot water through the system from an aerobic digester next door. I have fitted 6 contactor each using a switch wire from the thermostat to energise terminal 1 of the contactor, I have then linked from terminal one to a of the coil. I've taken a neutral to all contactor in parrelal in terminal 2 then from 2 to a2 of each contactor. I've then connected in parrelal the primary pump to terminals 3 and 4. This works fine with one stat, when it calls for heat aswell as energising the secondary manifold pump it also energises the contactor and energises the primary pump. The problem is, is that when another stat calls for heat if the other stat goes off the contactor still stays energised until all stats are off. I don't think it's latching contactor I'm sure there non latching could be wrong tho. I'm sure it's a wiring fault so any help would be great .
 
You will probably need relays. A sketch of what you have done will be good to see though. This diagram may help if you have a similar setup.
 

Attachments

  • [ElectriciansForums.net] contactor for underfloor heating
    image.jpg
    117.3 KB · Views: 164
OP - Can you tell me how many thermostats you have 6? - this is easy to wire - A1 to neutral, A2 switch live from the thermostat, put a permanent live into the contactor, load side of the contactor to boiler enable. The little pumps need to be connected to A2. The primary pump to boiler enable.
 

Reply to contactor for underfloor heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
988
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Update... I wired up my first heating system today! Thanks to all the help in this thread, (and the initial thread) I was completely prepared...
Replies
6
Views
1K
I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top