bennjy

Hi
I've installed the electrics for an underfloor heating system. The system has 6 manifolds each with a small pump. There is then a primary pump that pushes hot water through the system from an aerobic digester next door. I have fitted 6 contactor each using a switch wire from the thermostat to energise terminal 1 of the contactor, I have then linked from terminal one to a of the coil. I've taken a neutral to all contactor in parrelal in terminal 2 then from 2 to a2 of each contactor. I've then connected in parrelal the primary pump to terminals 3 and 4. This works fine with one stat, when it calls for heat aswell as energising the secondary manifold pump it also energises the contactor and energises the primary pump. The problem is, is that when another stat calls for heat if the other stat goes off the contactor still stays energised until all stats are off. I don't think it's latching contactor I'm sure there non latching could be wrong tho. I'm sure it's a wiring fault so any help would be great .
 
OK - repeat this at each manifold.

From a local switch fused spur bring Live & Neutral into a JB (small adaptable box), connect live into "2" connect the primery pump/boiler enable to "1"

Connect A1 to Neutral.

The switch live from the thermostat connect to A2 and also connect the live for the local pump to A2.

Make sure all the electrical feeds to the manifolds are fed from the same heating circuit.
 
Last edited:
Thanks for that. The way I've done it is to energise the coil with the switched feed then terminal 2 to primary pump but I guess that is enabling the contactors to stay latched once switched until all feeds are broken. I've mounted the time clock on a adaptable box so all cabling and contactors are in there. I've used 5 core tho so it's easy enough to do there
 
Thanks for that. The way I've done it is to energise the coil with the switched feed then terminal 2 to primary pump but I guess that is enabling the contactors to stay latched once switched until all feeds are broken. I've mounted the time clock on a adaptable box so all cabling and contactors are in there. I've used 5 core tho so it's easy enough to do there

Are there any valves?
 
Might have misenterpreted the OP but are you sure the "small pumps" are not actuator heads? Not sure contactors are needed here...

Otherwise what type of stats are you fitting and what rating are the pumps?
 
Last edited:
No its right as I just haven't wired them right for the job. There the same pumps as what you'd find in a domestic boiler install. It's one large area split into 6 zones. Each zone has a manifold and secondary pump. There is then a primary pump to get the water to all these pumps. I need it so when a stat calls for heat the primary pumps starts aswell as the manifold pump. It works but i wired the contactors wrong as they stay latched once another stat calls for heat. It's only when they all switch off that the contactors de-latch. Once the contactor is wired so there art any back feed to the pumps it will work fine.
Hope this makes sense
 
Thanks for the help. I understand how this should now be connected but because there wired in parallel at contact "1" will they not have a back feed and hold the other contras open once they have been enabled?
 

Reply to contactor for underfloor heating in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
401
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
988
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Update... I wired up my first heating system today! Thanks to all the help in this thread, (and the initial thread) I was completely prepared...
Replies
6
Views
1K
I think it was too early yes I meant 3 not 2, but great I'll give that a whirl and thanks.
Replies
8
Views
535

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top