W

whproject

My apologies all, my post was of coarse missing some stuff, and rather confusing.

1. Are there any obvious rules preventing the use of ring circuits coming from a contactor like the one pictured below, it doesn't s seem there is.

2 Provided there are no restrictions preventing the use of a ring circuit with said contactor, is the wiring on the diagram correct.

This 2 pole contactor is of coarse capable of a 63A load at point 1 and point 3 simultaneously correct or have I misunderstood something, what I am asking is hypothetically if 50A rated wire was used in the rings.

Then each ring circuit would be happy to draw 39A limited by the 40A breaker on each leg, correct? putting a 78A total load on the contactor, this is of coarse hypothetical, I know them breakers shouldnt be put under 90%+ load for x hours etc, I just want to be sure I have a full understanding of the workings of this contractor.
Thank you for you're time.
 

Attachments

  • [ElectriciansForums.net] Contactor---> Ring, wiring advice.
    contact.png
    436.5 KB · Views: 234
Last edited by a moderator:
Ive already noted the mcb rating and lack of rcd, the control from timer does not show how it is fused so can't comment the N don't need to be broken thus no need to run through contactor although its an option if you wanted to.

I can only assume the OP is learning possible early apprentice or DIY enthusiast due the set-up he chose to express his query and may not be an electrician although i will say he did express hypothetical but still to avoid critisism and create less confusion it would have been better with a standard circuit that complies as an example...
 
Last edited by a moderator:
Sorry, get the picture now, neutrals omitted I presume 2 x 40 amp RFC should be 32 amp cbs can't see any obvious flaws except the size of the cbs, what controls the coil?

The cbs will be 45A, the rings will be using 4mm rated at 32A and the draw on the rings will be well balanced/distributed along the ring, the rings load capacity will be safely over the 45A cbs, darkwood it will be an inductive load, but the 38A per ring will be on induction, I am 99.9% the ac3 rating of the contactor, (which I cant find) will be 50A+.

The wire from cbs to contactor will be 10mm rated at 55A
 
Can you give an example of a ring circuit in an industrial situation the only ones I personally have seen are to to with LV distribution systems is this what you mean?
 
Can you give an example of a ring circuit in an industrial situation the only ones I personally have seen are to to with LV distribution systems is this what you mean?

You can get 11kV Ringmains for a start, you might want to use a Ring Final circuit to connect a load of machine isolators up, it could depend on max cable sizes and circuit length for example, it may work out cheaper to install a ring distribution circuit.
There are many scenarios that could use ring circuits.
 
Agree with you but I'm a pedantic old fxxt and a ring final circuit as described in BS7671 is for 13amp socket outlets, maybe the phraseology used is confusing us both
 
Can you give an example of a ring circuit in an industrial situation the only ones I personally have seen are to to with LV distribution systems is this what you mean?
Can you give an example of a ring circuit in an industrial situation the only ones I personally have seen are to to with LV distribution systems is this what you mean?

Light runs in green houses.
Having a control board with points for each light and then individually wiring every light back to the board 900ft away is not feasible would take MASSIVE amounts of cable, more feasible would be having a dtrbn Ring on LARGE CAPACITY contacts running the length of the light run from the control board. and controlling a few 100 lights per switch.

PS I dont think I said "ring mains" in any of my post, sorryy for the confusion.
 
I need 38A per ring, of coarse there are plug sockets on teh ring, so my obvious option would be 4mm ring circuits, I will use 10mm rated at 55A from (45A mcb's) to contactor, this means each leg will start at a 45A breaker >>>55A cable to its own leg on the 63A contractor, to a ring of 4mm, rated at 32A, which will definitely have a higher capacity than the 45A breaker.

So just to summarise, bar the lack of RCD safety, using my diagram in the OP, with MCB and wire ratings from the above quote, this install would hypothetically, safely run 38A on each leg right.

Thank you all for you're time, and sorry for repeating myself and being annoying it's just of coarse I understand the seriousness and danger of electricity so just wanted to be 100% it would work (hypothetically of coarse)
 

Reply to Contactor---> Ring, wiring advice. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
648
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top