Continuity of Final Ring circuit | Page 2 | on ElectriciansForums

Discuss Continuity of Final Ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Im actually really excited too find out who se7aq is going to award this cream egg too.

Genuinley.
 
Im actually really excited too find out who se7aq is going to award this cream egg too.

Genuinley.

Me personally would like him to come back and say he has rectified his problem, then we can all take our right hand and place it on our left shoulder, Then give ourselves a pat on the back for being so helpful
 
try crossing your live and earth at the board. do a r1r2 test at every socket. the one with the highest reading check the connections. do the same for the neutrals then try you end to end readings again and see if you get better results.
 
Is your tester actually working??? L-L reading and N-N reading should at least be very similar if not exact same and E-E reading should be higher. Have you done a 'figure of 8' check? Could help determine an issue. You need to check connections at every point. Your high N-N reading suggests to me that a cable is barely touching the terminal. I am assuming you have done insulation resistance and got the all clear?
 
Hello Murdoch

Thanks for feedback. Yep, spot on, cheers, it was a loose connection in a socket, thankfully it was the first one I tried so thank you for the advice
Spent thousands trying to set up as a sole trador so starting to panic with my assessment and my mind is going blank.

Hay Murdoch, serious, I just won ÂŁ60 on the lottery, I'll round it up to ÂŁ100 (another ÂŁ40 won't make a differance with the amount I have spent lately anyway), name your charity (except bank of Murdoch) and I'll donate it to that chrarity with thanks to all on the Electricans Forum.
 
Hello Murdoch

Thanks for feedback. Yep, spot on, cheers, it was a loose connection in a socket, thankfully it was the first one I tried so thank you for the advice
Spent thousands trying to set up as a sole trador so starting to panic with my assessment and my mind is going blank.

Hay Murdoch, serious, I just won ÂŁ60 on the lottery, I'll round it up to ÂŁ100 (another ÂŁ40 won't make a differance with the amount I have spent lately anyway), name your charity (except bank of Murdoch) and I'll donate it to that chrarity with thanks to all on the Electricans Forum.

This forum isn't about money, its about contributing, asking questions, offering answers, showing your thanks, and likes.

Asking questions and not providing feedback just pxsses members off!
 
Hello chaps and chapettes,
Continuity of final ring circuit I measured:

L-L = 1.45
E-E = 0.8
but measuring N-N I got 108.8....???!!!!!!

Any ideas..? Or are those readings good in my limited experience and consequently I'm an idiot.

A out of date Cadbury's cream egg for the most sarcastic answer but a sensible one would be nice.


Calculate R1+R2 for me from the above!
 
Hello Murdoch

Thanks for feedback. Yep, spot on, cheers, it was a loose connection in a socket, thankfully it was the first one I tried so thank you for the advice
Spent thousands trying to set up as a sole trador so starting to panic with my assessment and my mind is going blank.

Hay Murdoch, serious, I just won ÂŁ60 on the lottery, I'll round it up to ÂŁ100 (another ÂŁ40 won't make a differance with the amount I have spent lately anyway), name your charity (except bank of Murdoch) and I'll donate it to that chrarity with thanks to all on the Electricans Forum.

You lucky Fu**** lol
 

Reply to Continuity of Final Ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
830
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
929

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top