se7aq

Hello chaps and chapettes,
Continuity of final ring circuit I measured:

L-L = 1.45
E-E = 0.8
but measuring N-N I got 108.8....???!!!!!!

Any ideas..? Or are those readings good in my limited experience and consequently I'm an idiot.

A out of date Cadbury's cream egg for the most sarcastic answer but a sensible one would be nice.
 
Not meaning to sound cheeky but if you don't know if those readings are good or bad and you don't know what would cause those readings then you should stop doing electrical work and go back to learning.
 
Nice one Murdoch you might win with that
end to end on L-L and N-N should be the same and E-E should be greater if the csa of earth is reduced to that of L-L.
if this is for an exam then make sure you use R1 for line Rn nutral and R2 for earth any way hope this helps .
 
Hello chaps and chapettes,
Continuity of final ring circuit I measured:

L-L = 1.45
E-E = 0.8
but measuring N-N I got 108.8....???!!!!!!

Any ideas..? Or are those readings good in my limited experience and consequently I'm an idiot.

A out of date Cadbury's cream egg for the most sarcastic answer but a sensible one would be nice.


They are Not very good readings to be honest (post was edited by admins, the original word is not acceptable on these forums) but it did rhyme with right.
 
Last edited:
Nice one Murdoch you might win with that
end to end on L-L and N-N should be the same and E-E should be greater if the csa of earth is reduced to that of L-L.
if this is for an exam then make sure you use R1 r1 for line Rn rn nutral and R2 r2 for earth any way hope this helps .


Corrections in red
 
Whats the problem there fine put it back together and walk away. I am sure a real spark will love the job to fix it after the fire.

(thats my entry for the creme egg!)
 
L-L should be within (*.**) of N-N. E-E should be *.** x greater than the the values you recieved for L and N if the cpc isn't the same as the conductors.

GN3 and OSG can be quite useful you know...
 
Leeds United are Short Sighted,
Never scored a goal in history...
They wear rubies on their boobies,
Sha la la la la, la la la la.

(bring back my childhood)
 

Reply to Continuity of Final Ring circuit in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
333
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top