This won't be the first daft posting of mine, but apparently once you get up to 20 postings you get additional privileges. So please treat me with contempt.

When testing a radial circuit you establish continuity of the Line and earth when you measure R1+R2. What test ensures continuity of the neutral conductor?

I brace myself for an answer that is going to confirm my question is a daft one.
 
You have in fact answered your own question.
If you do a temp link from earth to line and test along the length of circuit you have established continuity at each outlet, this will establish correct polarity of earth and line, following this we can assume that neutral is also established but there is no reason for you not to test that as well. Its not a daft question by the way. It shows that you are thinking about how you would confirm it is indeed verified.
 
R1+R2 is just 1 way to prove the continuity of the cpc, not the line. R2 only (using a wander lead) is equally acceptable.

That being said, if you really need to prove the continuity of the neutral I would say R1+Rn would be the best option. This way you can verify voltage drop at the same time.

Polarity can be proved while you're measuring R1+R2.
 
Jud have we been drinking the vino tonight ?
contradiction in your post I am assuming was because of the fine state you may be in.
 
R1+R2 is just 1 way to prove the continuity of the cpc, not the line. R2 only (using a wander lead) is equally acceptable.

That being said, if you really need to prove the continuity of the neutral I would say R1+Rn would be the best option. This way you can verify voltage drop at the same time.

Polarity can be proved while you're measuring R1+R2.

Thanks Jud. Understand your bit about R1+Rn. Please explain how this verifies votage drop. too tired to think through the logic.
 
Thanks Jud. Understand your bit about R1+Rn. Please explain how this verifies votage drop. too tired to think through the logic.

Using the resistance of R1+Rn you can work out the VD of the circuit.

VD = (R1+Rn) x Cr x Ib

Cr = Correction factor for conductor operating temperature
Ib = Design Current
 

Reply to Continuity of neutral conductor in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
904

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top