Link line and CPC at the CU gives you R1 and R2 how do you get RN is there and easy way.
Thanks
Mark
Link line and CPC at the CU gives you R1 and R2 how do you get RN is there and easy way.
Thanks
Mark
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Continuity of protective conductors in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi
how do you get RN is there and easy way.
Yeah, on a radial you dont bother
Functional tests will prove the neutral line
When you measure R1+R2, you also measure R1+RN. just cross connect line and neutral.
What's up with the KT61?
Is there a misprint in the Manual from Kewtech. On there website is says the KT 61 measures upto 200 MegOhms on insulation setting.
The sockets are on a ring also