Hi

doing R1 + R2 on lighting circuit green probe on cpc

Red probe on Switch line (switch ON) or Line.Which is correct? Switch line to confirm polarity? .took readings on both .why is switch line reading higher. Thank you for any replies.

Angus
 
I take it you have your temporary link at the DB? And you are measuring at the light fitting (ceiling rose?)? What are the readings you are getting?

You should be clipping to the switched line at both the switch and the light fitting (all relevant points on the circuit, recording the highest measured value). Measuring on the switch at the light fitting, operating the switch will confirm polarity.

The switch line at the light will usually be the highest reading (but not always!) because this is the longest length of cable, and you will always get resistance through the switch contacts.
 
You'll need to measure to the switch line to verify functionality of the switch and polarity. The increase in the resistance value is likely to be because of an increased conductor length.
Be aware of potentially higher measurements when you measure through a light switch, as these can sometimes introduce higher resistances from their poor contacts.
If you suspect a high value, then short out the light switch and measure again, seeing if the removal of the accessory itself has contributed towards a reduction in measurement.
 
Widdler, I'm not sure why you would want to short out the switch, unless you just want to prove that it is the switch and not a conductor or other termination that is introducing a high resistance? If the switch introduces an excessive element of resistance to the circuit then it should be replaced. If a switch is in a circuit it then forms part of the fault path, and as such needs to be included in measured values.
 
Ringer,

What widdler is trying to get at, is that if you do a con check on the switched line, and get a high reading, it could be due to the resistance of the switch contacts, i.e crap switch manufacturer. As you rightly state, the switch could become a problem, and would need replacing. Dead testing is not a science, and sometimes due to a variety of reasons we get iffy results. I would base my condition of the circuit by looking at the measured Zs, if its OK then its OK. I look upon R1 tests etc as a means to prove that i have continuity/polarity, but much else. I only take any notice if i get a stupidly high reading.

Cheers.......Howard
 
What exam are you taking? And for what examining body? Make sure you mention which it is before asking any more questions - will help us to give you the 'proper' answer (as expected by C&G etc, such as always do dead tests) rather than a practical real-life answer. Good luck in it anyway, whatever it is.
 

Reply to continuity of radial circuit conductors in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
301
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
813
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

I was at the other end of the results spectrum today. As I was driving home I had a call from my "Mrs Richards from Fawlty Towers" lady, very deaf...
2
Replies
20
Views
1K
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top