i=p/u

-
Arms
Joined
Dec 9, 2010
Messages
7,523
Reaction score
816
Location
Northern Ireland
i have a board which is protecting one side with 100A main switch, and the other side is being protected by 100A double pole rcd.

can i get another 100A rcd and put in as main switch which will cover the side un protected by rcd.[h=1]MEM/EATON 100Amp 2 Pole A100HE 100 Amp 30mA Double RCCB Breaker 100A RCD/RCBO[/h]
making this board 17th compliant then.

there is plenty of spare ways in this board so if i can get another 100A 30mA main switch and then mem mcbs for the new circuits, seems easiest than changing board ... trev
 
well i dont think i have ever finished a thread /post how it should be done.

i fitted new board for nearly same price as the rccb/rcbo that i needed to convert the mem board.. few heads is better than one so ty for guiding me to the harder option but better solution.

can i get anyone to confirm what test you carry out before you change a cu. ??? as you know im an apprentice but flying/ploughing on
 

Reply to converting mem board in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
123
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
970
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top