Afternoon all
Been asked to connect up cooker and Hob. Guy only has one 32amp cooker supply in 6mm. Has isolation point and connection point at low level
Spec for cooker is 2.4KW but has 13 amp plug fitted. So from that i read it as this cannot be connected up to 6mm connection point and has to have fused spur taken of kitchen supply and low level socket provided.
Hob is 16 amp and says requires hardwiring to dedicated circuit. Why would this be the case wouldn't it be adequate again to spur of kitchen supply and provide a connection point for this? Any advice appreciated