Afternoon all

Been asked to connect up cooker and Hob. Guy only has one 32amp cooker supply in 6mm. Has isolation point and connection point at low level

Spec for cooker is 2.4KW but has 13 amp plug fitted. So from that i read it as this cannot be connected up to 6mm connection point and has to have fused spur taken of kitchen supply and low level socket provided.
Hob is 16 amp and says requires hardwiring to dedicated circuit. Why would this be the case wouldn't it be adequate again to spur of kitchen supply and provide a connection point for this? Any advice appreciated
 
Cheers. Combined though they overrate the 32 amp breaker for cooker circuit don't they?. I Could spur out from low level connection point for cooker but where do I get my supply for hob. Sorry edit no this can't be case as only 16amp for hob although ratings for ring are 2.2kw 2kw 2kw and 2kw. I still can't see where I should fuse hob load though
 
Hi - the 16A hob doesn't need an additional fuse. If it was connected to the connection unit with a 3 core flex of 2.5mm (say) then the conductors can’t be overloaded and the cpc is the same size as the rest of the 6mm twin and earth radial circuit.

If I’ve understood correctly, the total load is 13+16=29A so that’s well ok too.
 
Hi - the 16A hob doesn't need an additional fuse. If it was connected to the connection unit with a 3 core flex of 2.5mm (say) then the conductors can’t be overloaded and the cpc is the same size as the rest of the 6mm twin and earth radial circuit.

If I’ve understood correctly, the total load is 13+16=29A so that’s well ok too.


Hob and oven are fixed load,
You can take both off the existing cooker feed if you want.

Cheers guys really appreciated will make sure get 2.5 heat resistant flex so will have 2.5 c.p.c
 
fit a cooker outlet for the hob and a socket for the oven, both from the existing 6mm 32A circuit. use one of these.
[ElectriciansForums.net] Cooker and Hob help
 

Reply to Cooker and Hob help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
796
  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top