Cooker cable | on ElectriciansForums
Discuss Cooker cable in the Australia area at ElectriciansForums.net
Cheadle,Stockport.
Hi all, just joined, starting my Nvq soon. Was wondering if I'm correct in assuming the cooker can be on a 6mm conductor on a 30amp RCD and the hood can be on 1.5mm if it's a spur?
Hi and welcome to the forum hope it will help you.
As your just starting then in most applications, and let's say it's a 6mm^ Twin + Earth cable it will be ok on a 32 amp protection device., but if it was in insulation exceeding 100mm thickness it would only take 27 amps, this is a rating factor you use when your designing a circuit, and you will be taught this.
Same as the use of RCD, RCB.RCBO, though you said 30 amp RCD you will find that it will either be in domestic situations a 63/80amp 30mA RCD with a 32 amp MCB or a 32 amp RCBO which is RCD/MCB combined, but again this will become clearer as you go along.
It is not normal to spur off of the cooker circuit to feed another aplliance ie a hood, as most manufacters advise a dedicated circuit for larger cooking appliances, the new modern under 3kw cookers can be treated differently but again let's not run before you can walk. A normal way to wire a hood would be to spur of the socket outlet circuit. So normally you would come of the socket in 2.5mm into a switched spur unit and then 1.5 or 1.00 to the hood, using a 3amp fuse in the switch spur
Not sure cooker power i was asked to fit cable on a first fix, I done his shower cable and said it should be ok for cooker too.
Sorry son who as asked you to do this, a friend, a relative or a sparks your working with. If it is a sparks then I hope he is guiding you as he should be, your not really ready to start taking decisions like this are you?
Reply to Cooker cable in the Australia area at ElectriciansForums.net
I actually did it with a 4 core 4.0mm swa last week!
Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic