Hi all, just joined, starting my Nvq soon. Was wondering if I'm correct in assuming the cooker can be on a 6mm conductor on a 30amp RCD and the hood can be on 1.5mm if it's a spur?
 
Sorry, i missed the bit where you mentioned fusing down anything mate....

I thought you said....300amp fused bus-bar..feeding an un fused 1.5mm cable (and if it is within a 3m length then thats okay) ?


But perhaps i misunderstood again.
 
Last edited by a moderator:
Sorry, i missed the bit where you mentioned fusing down anything mate....

I thought you said....300amp bus-bar....3m....1.5.


But perhaps i misunderstood again.


You did understand it correctly. The point is yes you can do it (in fp200 cable) the thing is would you do it? NOT A CHANCE. It would be like wiring your cooker up using 6A fuse wire, it would go bang soon as a fault occurred.
 
You did understand it correctly. The point is yes you can do it (in fp200 cable) the thing is would you do it? NOT A CHANCE. It would be like wiring your cooker up using 6A fuse wire, it would go bang soon as a fault occurred.



Under fault conditions, 1.5 mm cable, connected directly to a 300amp bus-bar wouldnt go 'bang'.....well, it might go 'bang' but it would definately burn, and so would everything combustible around it.

aye.

Melt.
 
Last edited by a moderator:
yes i want to learn , and i pretend i know sometimes but just have idea. but you can come off busbar in say1.5mm into fused connection with 3m..


Please mate let's not go backwards, as before yes but its done in industrial installations.

Another thing ipu is that people come to this forum for help and advice and if anyone looks at what you have written will think its ok to connect any size cable to a busbar in a house and end up setting it on fire or frying themselves. It's good to ask or debate what we don't understand but better to give a full answer so there is no misinterpretation and everyone is safe.
 
drink bad for you. ok.. its not good point at all but the fuse within 3m would protect the cable and any fault current should be cleared before gets to high temp. is why its allowed. im not even sure if il ever come across it. case closed. you got a straw after listen to me
 
The point is, the 3m of 1.5mm is protected by a 300A fuse and therefore not protected at all. The FCU would only be protecting the cable after the FCU. What would happen if someone damages the 3m of cable with a nail? How many amps would they get? I bet the cable would burn out first but by that time your dead!
 
has to be in enclosure (mechanical)


But didn't you say earlier that it would be cheaper just to run the 1.5 from the busbar to the FCU? Now with mechanical protection the price on parts and labour are going up. Let's face it, shall we just use a mcb from the busbar to the appliance, there we go nice and simple and cheaper. Or if there isn't a spare mcb, tail off the busbar to a 2nd c/u or stand alone mcb via a double pole isolation switch. That's the correct application for the use of a cable coming from a busbar within 3m, not a spur to a cooker hood.
 

Reply to Cooker cable in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
803
Although it might appear that I am being elusive with the facts, the point is, only you know what your worth is per hour and how long it will...
    • Optimistic
Replies
3
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top