Since when did your hob turn into a cooker?![]()
hi al,Since when did your hob turn into a cooker?
Flukey, don`t get all paranoid on me now.![]()
You can`t go back to the Darkside now! With those that have not yet seen the light - stand with me & we`ll convert em
"What you say? 16mm for a cooker! Ahh, we have to route it through a foundry. Quite right. Will be 16mm then"
Flukey, 10mm sounds fine. Unless you are routing through a foundry that is![]()
meant to say oven not cooker.
hi al,Don`t get going paranoid again
Kinda proves the point re: assessing demand & diversity really.
But where we were estimating the actual load wouldn`t reach the supplied max rating, being the manufacturer they know it can`t by its design, and have thus suggested using a lower ccc supply cable.
Must admit tho, 2.5mm seems a bit optimistic. Were they specific about type of cable? 6.8w / 240v would allow 28.3 A tops, so assuming thermostatic control, real-world current draw = less than that most likely.
Ultimately its up to you fella, & Manufacturers Instructions are usually Bible, but if you`re uncomfortable with 2.5mm theres nothing wrong with going bigger.
16mm it is then![]()
hi pennywise,Because when you alow for diversity on the hob unit it gives you a figure of 22.8 amps or 23.6 if your using 230v for your calcs, the manufacturer has given the minimum size of the supply cable as 2.5mm because probably it's only taking into account the possibility of the cable being clipped to the wall direct and so giving it a maximum current carrying capacity of 27amps they don't take into consideration the installation method because that is our job to identify the factors that should be applied hence you would probably wire the hob in a minimum of 4mm which would take into consideration it being buried in the wall,in insulation or volt drop etc. Sure someone will correct me or have a different view thanks.