OP
The hob igniter... is it a big (relatively) push button or is it a touch control?
Neither, it automatically sparks when you turn the know for the gas ring.
Discuss Cooker hood trips other circuits on fuse board: what's going on? in the The Welcome Forum area at ElectriciansForums.net
I'll try again.
Op has it worked properly since the kitchen works?
So that's a no then!
Can you post a picky of your fuse board?
A appliance on circuit 4 tripping circuits 5 and 6 sounds implausible
You have a cooker hood outlet that trips the up and down sockets,because it is located in the kitchen may not mean it is part of the kitchen ring
If it was wired into both the up and down ring (bridging both)it may be possible to operate a very low current appliance much of the time and perhaps cause tripping of one or both the Up and/or the Down Rcbos on occasion only,the imbalance of the trip may be within its threshold with just a fan
The hob igniter operating when it feels like doing so is very strange and other than guessing its some sort of capacitive charge across a faulty item then I would be at a loss to even consider this is real
Don't know if anyone else has asked, and my head hurts when I try to read back through the posts, but these 3 Electricians that have looked at your problem, did they leave any reportsafter they hAD
OP from what you've described, your faulty (possibly) cooker hood is tripping circuits 5 or 6, when logic suggests it should be tripping circuit 4, i.e. kitchen sockets? Unless the kitchen fitter, pinched a supply from the upstairs ring to feed the cooker hood?
Think the sparking hob thing is artistic licence, and too much wine when cooking
You could unplug your cooker hood temporarily, and see if that stops the fault.
Why don't you first try disconnecting the cooker hood by turning off at the wall switch you mention. This should be a double pole switch, which should electrically disconnect it from it's supply. If the fault not longer manifest itself, then you could start looking at having the appliance tested for faults.
This does not explain why the hood on circuit 4, is tripping circuits 5 & 6. Sometimes with the best or worse intentions, kitchen fitters deputise themselves as electricians, and can make a right hash of things, this of course is not true of all kitchen fitter electricians. If, as it already has been suggested, these circuits have been cross connected, may be one possible line of inspection.
I note that your fuse board is populated with MEM ALB321 mcb's. I don't believe you could purchase an MEM ALB321 RCBO (Residual Current Breaker with Overcurrent)? You can however, I'm told, convert them to an RCBO, using a field fit RCD Pod. MEM are no more, but spares are obtainable from EATON, well not spares but replacements. Clutching at straws, perhaps these kits have not be assembled as per manufacturers instructions?
You seem to have some confidence & trust in the electrician who originally rewired your property. Why don't you see if he/she will come back and investigate these faults?
It is difficult to carry out fault finding from afar. The label on your fuse board suggest you are due an inspection anyway.
Fair comment. It's just that after having had 3 competent* local sparks draw blanks I thought I'd try a different tack for some input. Which I've gotYou won't diagnose and fix this on a forum. You need a competent local spark with time, a mft and a clamp. Meter......
And money to pay them