I'll try again.

Op has it worked properly since the kitchen works?

The extractor has tripped those other two circuits for as long as I can remember but I can't swear whether it started as soon as we had the kitchen fitted or not, sorry. I can't think of any work that's been done or anything that's happened since the fitting that may have triggered the phenomenon. Ditto the hob sparking thing.
 
Don't know if anyone else has asked, and my head hurts when I try to read back through the posts, but these 3 Electricians that have looked at your problem, did they leave any reportsafter they hAD
 
A appliance on circuit 4 tripping circuits 5 and 6 sounds implausible
You have a cooker hood outlet that trips the up and down sockets,because it is located in the kitchen may not mean it is part of the kitchen ring

If it was wired into both the up and down ring (bridging both)it may be possible to operate a very low current appliance much of the time and perhaps cause tripping of one or both the Up and/or the Down Rcbos on occasion only,the imbalance of the trip may be within its threshold with just a fan

The hob igniter operating when it feels like doing so is very strange and other than guessing its some sort of capacitive charge across a faulty item then I would be at a loss to even consider this is real
 
So that's a no then!

Can you post a picky of your fuse board?

I did this already but it looks like the server move may have lost it so here it is again.

IMG_4050.JPG
 
A appliance on circuit 4 tripping circuits 5 and 6 sounds implausible
You have a cooker hood outlet that trips the up and down sockets,because it is located in the kitchen may not mean it is part of the kitchen ring

If it was wired into both the up and down ring (bridging both)it may be possible to operate a very low current appliance much of the time and perhaps cause tripping of one or both the Up and/or the Down Rcbos on occasion only,the imbalance of the trip may be within its threshold with just a fan

The hob igniter operating when it feels like doing so is very strange and other than guessing its some sort of capacitive charge across a faulty item then I would be at a loss to even consider this is real

If I manually flick off the fuse for circuit 4 the extractor fan stops; not so with circuits 5 & 6.

When you say you would be at a loss to even consider this is real (hob sparking), do you mean you don't believe it happens? Cos it does! :)
 
OP from what you've described, your faulty (possibly) cooker hood is tripping circuits 5 or 6, when logic suggests it should be tripping circuit 4, i.e. kitchen sockets? Unless the kitchen fitter, pinched a supply from the upstairs ring to feed the cooker hood?

Think the sparking hob thing is artistic licence, and too much wine when cooking :)

You could unplug your cooker hood temporarily, and see if that stops the fault.

Why don't you first try disconnecting the cooker hood by turning off at the wall switch you mention. This should be a double pole switch, which should electrically disconnect it from it's supply. If the fault not longer manifest itself, then you could start looking at having the appliance tested for faults.

This does not explain why the hood on circuit 4, is tripping circuits 5 & 6. Sometimes with the best or worse intentions, kitchen fitters deputise themselves as electricians, and can make a right hash of things, this of course is not true of all kitchen fitter electricians. If, as it already has been suggested, these circuits have been cross connected, may be one possible line of inspection.

I note that your fuse board is populated with MEM ALB321 mcb's. I don't believe you could purchase an MEM ALB321 RCBO (Residual Current Breaker with Overcurrent)? You can however, I'm told, convert them to an RCBO, using a field fit RCD Pod. MEM are no more, but spares are obtainable from EATON, well not spares but replacements. Clutching at straws, perhaps these kits have not be assembled as per manufacturers instructions?

You seem to have some confidence & trust in the electrician who originally rewired your property. Why don't you see if he/she will come back and investigate these faults?

It is difficult to carry out fault finding from afar. The label on your fuse board suggest you are due an inspection anyway. :)
 
Why don't you first try disconnecting the cooker hood by turning off at the wall switch you mention. This should be a double pole switch, which should electrically disconnect it from it's supply. If the fault not longer manifest itself, then you could start looking at having the appliance tested for faults.

This does not explain why the hood on circuit 4, is tripping circuits 5 & 6. Sometimes with the best or worse intentions, kitchen fitters deputise themselves as electricians, and can make a right hash of things, this of course is not true of all kitchen fitter electricians. If, as it already has been suggested, these circuits have been cross connected, may be one possible line of inspection.

I note that your fuse board is populated with MEM ALB321 mcb's. I don't believe you could purchase an MEM ALB321 RCBO (Residual Current Breaker with Overcurrent)? You can however, I'm told, convert them to an RCBO, using a field fit RCD Pod. MEM are no more, but spares are obtainable from EATON, well not spares but replacements. Clutching at straws, perhaps these kits have not be assembled as per manufacturers instructions?

You seem to have some confidence & trust in the electrician who originally rewired your property. Why don't you see if he/she will come back and investigate these faults?

It is difficult to carry out fault finding from afar. The label on your fuse board suggest you are due an inspection anyway. :)

Thanks, Midwest: all sound advice. I think I will get our original sparky back and run everyone's suggestions past him. I'm pretty sure he tested to make sure that the three circuits in question were properly independent of each other bu there might be something he hasn't thought of. You're quite right about an inspection being due too: I only noticed that when I posted the photo! Slightly embarrassing...
 
You won't diagnose and fix this on a forum. You need a competent local spark with time, a mft and a clamp. Meter......

And money to pay them

P.s. I'm sure those are rcbo's
 
You won't diagnose and fix this on a forum. You need a competent local spark with time, a mft and a clamp. Meter......

And money to pay them
Fair comment. It's just that after having had 3 competent* local sparks draw blanks I thought I'd try a different tack for some input. Which I've got :)
* Though I guess some might measure competency by the ability to sort out the problem...!
 

Reply to Cooker hood trips other circuits on fuse board: what's going on? in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

You may still have a problem with earth leakage though, it could be that the Samsung has less leakage than the Bosch ones. If you do get a random...
Replies
13
Views
2K
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
697

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top