Can u run a 6 mm cable for hob 32 amps and 2.5 cable 16 amps off same cooker switch , 45 amp cooker switch wired on own circuit back to cu on 32 amp breaker.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Cooker installation advice in the UK Electrical Forum area at ElectriciansForums.net
Thanks for your replyJust fit one of these.
Scolmore 45A EASYFIT DUAL APPLIANCE OUTLET PLATE
The Scolmore PRW217 45A Easyfit Dual Appliance Outlet Plate are a polar white accessory ideal for use around the home or office.www.superlecdirect.com
As said dual outlet. Click do a gooden.Noted, it’s just about where both appliances are terminated , can u feed them both to one cooker switch.
No problem. One cable to the dual outlet and connect both appliances to it with diversity applied they will rarely achieve that for a sustained period.10.8 KW combined
On this occasion, 32A + 16A =48A
The other options are probably not available.
What did the electrician that came out say?
After all they have the best information and knowledge of the installation.
applying diversity to 48A. ( 10A+ (38A x 0.3)) = 21.4A. add 5A if isolator has a built in socket.On every occasion 32 + 16 =48,thats a simple mathematical truth.
However that is not the correct way to calculate th eload on this circuit, you need to apply diversity.