Installing first fix wiring in a new build and the kitchen will have a range cooker. There is no mains gas and bottled gas is not desirable. The cooker will therefore be all electric with an induction hob. The manufacturers website (Rangemaster) have a MAX load on the cooker of 17.4KW (around 75A). I have discussed this with their technical department and they have advised that as it's a domestic premises, you can apply diversity and therefore the working load is around 30A. They recommend putting the cooker on it's own dedicated 45A breaker with a 10mm2 cable. They have also stated these have been installed in a number of domestic premises without issue using the above recommendations.

Any thoughts on the above? :confused:
 
well diversity for a cooker is normally 10a + 30% of full load + another 5amp if there is a socket on the control unit

So it would be 10a + 30% of the FL as you say 75amp so would be 32,5amps + the 5amp if it as a socket.

Your 45amp could be a 40amp and stick with the !0mm^ but make sure that the 10mm^ will be enough if there are any de-rating factors.
 
I can't see a problem here, don't bother with the socket, but check that your consumer unit is up to the task (I think some old wylex units had a max of 60A total load) especially if you have an electric shower etc etc.
Contactor switching is often used in this situation but doesn't really comply with requirements for isolation.
 
It's a brand new Wylex CU rated at 100A. No intention of putting a socket on it. No electric showers either.

I was going to run the cooker off a contactor controlled via a grid switch. The contactor would have normally open contacts but when the grid switch was on, the cooker would be powered. Any problems with this arrangement?
 
No it doesn't. The point is I don't want an ugly cooker isolation switch and would rather control all the appliances from one grid switch. The grid switch ratings only go to 20A but utilising one of these through a contactor mounted either within the CU or next to it would allow control of the cooker via the grid switch.
 
no problem in putting cooker isolator inside kitchen unit, as long as it's accessable and within 2m of the appliance
 

Reply to Cooker Load in New Build in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
361
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
918
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top