Copper bath, bond or not? | on ElectriciansForums
Discuss Copper bath, bond or not? in the Australia area at ElectriciansForums.net
jedisparks
Evenin all!
hope ive put this in the correct forum, apologies if not.
doing a domestic job at the moment and the customer has had the bright idea of having a copper bath installed. The taps are fitted to the wall and the waste is plastic. do i need to bond the bath. im thinking not, as long as the bathroom circuits are rcd protected. im just concerned.
what do you think?
many thanks in advance
The bath itself will only need bonding if it is in contact with structural steelwork....otherwise metallic sevices entering the bathroom will require supplementary bonding unless the 3 conditions to omit are met.....1 All circuits within the bathroom are protected by a 30ma rcd....2 required disconnection times are met....3 a continuity reading of less than 1667 ohms is obtained between conductive and extraneous conductive parts within the bathroom.....Pay attention in particular to the definition in the BRB of extraneous conductive parts,this is where most of the confusion arises,generally a copper bath would not be an extraneous conductive part but copper pipes supplying it may well be.
Reply to Copper bath, bond or not? in the Australia area at ElectriciansForums.net
    • Friendly
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Switch by the door, pendant holder and a 100W bulb, some will remember, others weren't born yet when it went out of fashion, but this was the...