anyway you shouldn't have two rcd's in line unless they are of different rataings (I an)

Not even then, unless your talking about 500mA upstream and 30mA downstream. I've even seen that arrangement trip out together, if the leakage has been excessive...
The only sure way of achieving discrimination between RCD devices is by time delay!!
 
Do you have 3 neutral bars in the house CU? If so then put in a 100mA Time delay S type RCD (bit pricey though) and run the shed/cabin supply mcb off this....you could then use a 30mA RCD in the shed/cabin and have discrimination - should a fault develop in the shed/cabin then only the 30mA RCD in the CU there will trip without taking the house out. The cable run from the house to the shed/cabin is also RCD protected.
 
I've had a proper look at job today I think I'm going with split tail small enclosure with double pole isolater feeds 32amp mcb which feeds armoured to cabin where I'll fit the small garage type enclosure 63amp 30milliamp rcd switch feeding 20 and 6 amp mcb. Cheapest way and easier of options to install. Cheers for feedback
 
sounds like a plan. just need to decide whether to use 2 coreSWA using armour as cpc or 3 core. ( or even to TT the garage ). i would deffo use 6mm to allow for possible increase in demand.
 

Reply to Correct discrimination? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
391
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
975
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Do you know what percentage of scheme registered electricians are registered to sign off 3rd party work? Even better would be a poll of how many...
2
Replies
25
Views
2K
nicebutdim
N
Why go to the trouble of adding another cable, which I assume would follow the same route as the other ?. Why not upgrade it. It was to try to...
    • Like
Replies
1
Views
190

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top