anyway you shouldn't have two rcd's in line unless they are of different rataings (I an)
Not even then, unless your talking about 500mA upstream and 30mA downstream. I've even seen that arrangement trip out together, if the leakage has been excessive...
The only sure way of achieving discrimination between RCD devices is by time delay!!