Correct way to install an earth rod. | on ElectriciansForums

Discuss Correct way to install an earth rod. in the UK Electrical Forum area at ElectriciansForums.net

M

Millboy

Hello people. This week I've got to install a rod at a property where the gas is being used as the main earth. I've installed them before for temporary generators etc but never done a permanent one. I'd be grateful if someone with more experience could help.

The house is surrounded by concrete, so I'm thinking drill through that close to the house, bash the rod down, and screw an adaptable box to the floor with the connection inside all labelled up. Then 16mm clipped a short way and through into where the board is.

Thanks guys.

Ps its an overhead supply.
 
Come away from the house at least a metre and sink your plastic pit, take some (ie more than 1) coupleable 5/8 rods and start driving them down get 2 in then test your Ra, if its high go get another 1 from the wholesalers and start driving again. Repeat as necessary till you get a nice low reading
 
Hello people. This week I've got to install a rod at a property where the gas is being used as the main earth. I've installed them before for temporary generators etc but never done a permanent one. I'd be grateful if someone with more experience could help.

The house is surrounded by concrete, so I'm thinking drill through that close to the house, bash the rod down, and screw an adaptable box to the floor with the connection inside all labelled up. Then 16mm clipped a short way and through into where the board is.

Thanks guys.

Ps its an overhead supply.

and wait for a call from E54
 
you'll need 5/8 rods and connectors - take 3 sets minimum. If the reading is still high it could be because the ground is so dry, so take a watering can too (or use your own)!!
 
I hate typo, always get the feeling Im being sarky or somethng, nethertheless, Im just asking....

No mention so far of cable avoidance tool usage.

Guessing as youve identified the overhead incomer and its routing theres no need, ok sorry, just thought Id ask
 
My fear is always with hitting a drain or storm drain pipe as the services are normally easy to find but drains seem to run anywhere and not always with indications on direction of run on older properties. a couple i've done I cringed with every smack the the hammer.
 
My fear is always with hitting a drain or storm drain pipe as the services are normally easy to find but drains seem to run anywhere and not always with indications on direction of run on older properties. a couple i've done I cringed with every smack the the hammer.
a good giveaway would be manhole and access covers and the like......stench pipes and drains....
 
I wouldn't worry about drains, they don't bite back, I always worry about hitting a stray MV distribution cable.

There's always a remote chance you might hit something unexpected but if you carefully dig a hole about a meter (3-4 feet) deep before you start whacking in the rods you should reduce the chance considerably.
 
What can i say!! All that needs to have been said, ...has been said!! lol!! And not a single mention to date, of that junk 200 ohm Ra, ...I'm impressed, i really am!! ...lol!!

The only thing i can add, is try driving in those rods with a rotary stop SDS, it really is much quicker and your not left with a big hole at the entry point from the flexing of the rod each time you hit the thing with a club or sledge hammer!! Don't forget to buy the driving head/pin that threads into the rod connectors....
 

Reply to Correct way to install an earth rod. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top