Hello people. This week I've got to install a rod at a property where the gas is being used as the main earth. I've installed them before for temporary generators etc but never done a permanent one. I'd be grateful if someone with more experience could help.

The house is surrounded by concrete, so I'm thinking drill through that close to the house, bash the rod down, and screw an adaptable box to the floor with the connection inside all labelled up. Then 16mm clipped a short way and through into where the board is.

Thanks guys.

Ps its an overhead supply.
 
What can i say!! All that needs to have been said, ...has been said!! lol!! And not a single mention to date, of that junk 200 ohm Ra, ...I'm impressed, i really am!! ...lol!!

The only thing i can add, is try driving in those rods with a rotary stop SDS, it really is much quicker and your not left with a big hole at the entry point from the flexing of the rod each time you hit the thing with a club or sledge hammer!! Don't forget to buy the driving head/pin that threads into the rod connectors....
Agreed and more importantly the rod doesnt move and you end up clubbing yourself,also in relation to the bible bashers tell them your a satanist I did and I,ve never seen anything go down my drive as fast that wasn,t followed by my large GSD lol.
 
My fear is always with hitting a drain or storm drain pipe as the services are normally easy to find but drains seem to run anywhere and not always with indications on direction of run on older properties. a couple i've done I cringed with every smack the the hammer.

At least if you go through a drain, the readings should stay nice and low :innocent:
 
Well it went ok apart from the snow! Tw*tted 3 down and ended up with 24.3ohms which I'm fairly happy with. I like the tip about getting them down with an sds drill but that would only work with the smaller rods as far as I can see. Yes I was a bit scared of hitting something as there could be anything that deep, unexploded bomb crossed my mind lol!
 
That's the worry with earth rods for me.

In the the UK you never know what is under the ground or how far to risk digging, putting in an earth rod is a night mare really, the damage you could do if you hit something could cost you a fortune, how can you tell what's down there?

I'm not a scaremonger but if I drove a rod down around here I would always be worried what I would hit.

I guess that's why the skinny little rods are so popular.
 
Well it went ok apart from the snow! Twitter 3 down and ended up with 24.3ohms which I'm fairly happy with. I like the tip about getting them down with an sds drill but that would only work with the smaller rods as far as I can see. Yes I was a bit scared of hitting something as there could be anything that deep, unexploded bomb crossed my mind lol!

Why do you think that?? That's exactly how the professionals drive rods in the ground where the soil type is known to be good!! OK, they will be using heavier duty equipment than most electricians will carry, but then they will be probably going down a lot further than you intend too, ...like 6 to 9m!! What you need is an old socket that fit's over the driving tip and rod connector that's welded/brazed onto an old SDS drill shaft or similar. I still have mine, that i had made for me over 15 years ago... My one is for 3/4'' rods, but probably also good for 5/8'' rods too, if a bit of a sloppy fit...lol!!
Or of course, you can buy a propriety off the shelve job, but some can be on the expensive side... lol!!

Those thin rods are are next to useless far too thin and far too short, and can't be extended!!! They should be removed from the market place altogether full stop!! lol!!
 

Reply to Correct way to install an earth rod. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top