banny07

-
Arms
Joined
Aug 2, 2009
Messages
193
Reaction score
39
I had a message from a customer to sort out tripping akitchen circuit mcb. I asked him when was installation tested. He sent me a satisfactory EICR page. Under general condition it says high Zs reading. Ze is 7.25ohm. Could it be misprint? what are your thought guys.
 
Last edited by a moderator:

Attachments

  • [ElectriciansForums.net] could it be misprint?
    forum.jpg
    332 KB · Views: 74
  • [ElectriciansForums.net] could it be misprint?
    forum2.jpg
    210.1 KB · Views: 75
Having a PFC of 30A would not trip the MCB on a L-E fault, but it could trip a RCBO.

However it could be a L-N fault that would take out the MCB as the supply PSCC would normally be something of the order of 600A or more (and ought to go in that table as the max value that the fuses/breakers have to clear).

EDIT: As above, double check the earthing as ~30A on any TN systems is seriously bad. Usual assumption is max 0.8 ohms but that is not set in stone, but supply fuse clearing should be considered.
 
However it could be a L-N fault that would take out the MCB as the supply PSCC would normally be something of the order of 600A or more (and ought to go in that table as the max value that the fuses/breakers have to clear).
I was thinking this, and also that whoever filled out the paperwork surely can't have taken the maximum of PEFC and PSCC for the PFC value...
Or to put it another way, if PSCC is that too then there's an even more serious condition pending....

The OP put on another thread he is fairly new to testing, and he's getting a lot more than his fair share of interesting situations. Hopefully he'll get some normal functional installations to test eventually! Otherwise "High Zs Specialist" will be on his business card soon....
 
The EICR bits shown don't have any final circuit Zs values for additional confirmation of its TT-ness.

It also possible that extraneous bonding is bringing the Zs at DB down to a low enough value as well (crap earth cable / cut-out here, but neighbours pipework bonded on good TN-C-S sort of thing).
 
EDIT: As above, double check the earthing as ~30A on any TN systems is seriously bad. Usual assumption is max 0.8 ohms but that is not set in stone, but supply fuse clearing should be considered.
Having looked around for the answer to the max Ze related to the supply fuse I found this:

Why on a TN-S earthing system is the maximum Ze given as 0.8 ohms by the supply authority when it’s often protected by a BS 88-3 100A fuse which has a maximum Zs of 0.38 ohms?

This maximum value for Ze of 0.8 ohms for a TN-S earthing system is a value that is quoted by the distributor and is commonly used for calculating likely Zs values within an installation at the design stage.

The main reason why you don’t need to change the BS 88-3 fuse within the supply cut-out when you have a measurement above the maximum value of 0.38 ohms for a 100A BS 88-3 fuse (T41.4) is because the Zs values given in the tables 41.2 to 41.4 BS 7671: 2018 are for protective devices providing fault protection (automatic disconnection in case of a fault).

The main fuse at the cut-out position is only providing overload protection for the incoming supply conductors. Fault protection is provided by the individual circuit breakers, fuses etc within the consumer unit which also provide individual overload protection for their own circuits.


So it seems the DNO side has no specific ADS requirements like a sub-main would. (If anyone with DNO knowledge can add to the please do so!) The related NICEIC guide booklet is here:
 
Think they have simple put the ze reading and PFC value the wrong way round . Ze is 0.03 ohms Pfc is 7.25 ka
I did wonder about that too, but there’s a comment about high Zs readings on the report, and unless the supply voltage was about 217 volts it seems that the maths don’t quite stack up.
Sadly I think it’s more likely there’s a problem.
 
I did wonder about that too, but there’s a comment about high Zs readings on the report, and unless the supply voltage was about 217 volts it seems that the maths don’t quite stack up.
Sadly I think it’s more likely there’s a problem.

I did wonder about that too, but there’s a comment about high Zs readings on the report, and unless the supply voltage was about 217 volts it seems that the maths don’t quite stack up.
Sadly I think it’s more likely there’s a problem.
Yes sorry does not look like that. May be worth getting a picture of the main head to give you a clue if it maybe TT
 
It would be interesting to see the whole EICR, if available. Apart from presumably not measuring PSCC, when putting down a value for PFC, I'm curious why the next inspection for what I presume is a domestic property with wiring only 11 years old is due after only another 2 years. Unless perhaps this is not a domestic property?
 

Reply to could it be misprint? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This is very common. Most Kitchen fitters & Builders all do this. They get your quote, whack on 50% and tell their client the new price. Then get...
    • Like
    • Optimistic
    • Winner
2
Replies
20
Views
1K
Thanks for the reply littlespark. Yes the works have been carried out. Surely it is fraudulent because basically the document is Not...
Replies
2
Views
718

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top