Right or wrong please? , if wrong, what needs to be done to fix it? thanks in advance.
[ElectriciansForums.net] Could someone please tell me if this is right or wrong please.
 
Last edited by a moderator:
Very wrong.
dangerous
and untidy.

I can’t see a single cable that has been landed and terminated correctly.
it needs ripping out and doing again, your average first year apprentice would do a better job than that.
 
The supply is using black as neutral and blue as a line. I would seriously question the competence of someone who cannot even get that correct.
I am wondering how much of this photo is new and how much old?

I.e. maybe it was old colours with black on the neutral bar, and someone has used new colour SWA and got their undergarments in a twist trying to work out what to do.

If it was old colours and new SWA, then blue tape on the existing neutrals and putting in the new colours correctly would be the right thing to do. The other tape also is not quite right, if they were using yellow to identify L2 and blue for L3 then why no red for L1? And why not use the new colours correctly?

And while it is good to leave enough slack so the next spark can re-terminate without stress is excellent practice, it should not be enough to hang yourself with!
 
I am wondering how much of this photo is new and how much old?

I.e. maybe it was old colours with black on the neutral bar, and someone has used new colour SWA and got their undergarments in a twist trying to work out what to do.

If it was old colours and new SWA, then blue tape on the existing neutrals and putting in the new colours correctly would be the right thing to do. The other tape also is not quite right, if they were using yellow to identify L2 and blue for L3 then why no red for L1? And why not use the new colours correctly?

And while it is good to leave enough slack so the next spark can re-terminate without stress is excellent practice, it should not be enough to hang yourself with!
Hi, it is a new installation, not in the UK, unfortunately this is what have to deal with, so looks like i need them back in and to do it correctly as per all the comments and suggestions above, thank you for the advise.
 
Hi, it is a new installation, not in the UK, unfortunately this is what have to deal with, so looks like i need them back in and to do it correctly as per all the comments and suggestions above, thank you for the advise.
Dare I ask where?

i.e. to what national standard should it be constructed/installed?
 
Dare I ask where?

i.e. to what national standard should it be constructed/installed?
Supposed to be to British standards, unfortunately, everyone seems to be an engineer over here in Lagos Nigeria, even the people who work in the markets, I knew a lot was wrong with the DB even though I'm not a spark, but you guys have highlighted so much more.
 
In the uk we would expect the correct glands to be used for each of the armoured cables so the armour is earthed.
this has not been done on any of the cables visible in the photo.

uk spec would be
L1 brown
L2 black
L3 grey
N blue

if the cables are terminated correctly at the other end and incorrectly (as shown) at this end then 2/3 of the single phase equipment is likley to be destroyed and the remaining 1/3 is dangerous as the N will be switched instead of the live so the circuit breaker of fuse will break the N not the live in the event of a fault.
 
In the uk we would expect the correct glands to be used for each of the armoured cables so the armour is earthed.
this has not been done on any of the cables visible in the photo.

uk spec would be
L1 brown
L2 black
L3 grey
N blue

if the cables are terminated correctly at the other end and incorrectly (as shown) at this end then 2/3 of the single phase equipment is likley to be destroyed and the remaining 1/3 is dangerous as the N will be switched instead of the live so the circuit breaker of fuse will break the N not the live in the event of a fault.
Thanks James, that's very helpful, give s me loads to get sorted now, fingers crossed for a safe outcome.
 

Reply to Could someone please tell me if this is right or wrong please. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

@DefyG is right... I'm not fully sure what your boss is after as when doing single line diagrams I usually show the whole installation. Anyhow I...
Replies
4
Views
405
Ignore the post in #3 it is of no help. Hopefully someone may know but it maybe a longshot, have you asked on a more specific appliances forum?
Replies
2
Views
418

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top