couple of questions just thought I would run them by you lot to see your thoughts

1. Changing a fuseboard and it's in a block of flats the supply comes in 10mm singles through a conduit then a meter then 16mm tails to the board.

Bonding is all in place and tested it's 6mm though. Planning to leave this as is.

Feels wrong to use the old painted tails so going to upgrade them to 25mm

Should the bonding be upgraded as I've upgraded the tails. I think not as the supply is 10mm

Should I buy new 16mm tails ? would rather not as I have lots of 25mm

2. Changing another board and all the cables are rear entry including tails.

Anyone see any problem cutting a big square cutout at the back for the cables and tails

Normally I use a stuffing gland at the bottom to hold the tails still

Only thought is the tails are free to move about in free air not that there should be movement but I carnt think how to secure them when they are coming in from behind.

Not enough slack to put a stuffing gland at the back and tighten and place the board to the wall

The current board has them like this floating about.

Cheers
 
couple of questions just thought I would run them by you lot to see your thoughts

1. Changing a fuseboard and it's in a block of flats the supply comes in 10mm singles through a conduit then a meter then 16mm tails to the board.

Bonding is all in place and tested it's 6mm though. Planning to leave this as is.

Feels wrong to use the old painted tails so going to upgrade them to 25mm

Should the bonding be upgraded as I've upgraded the tails. I think not as the supply is 10mm

Should I buy new 16mm tails ? would rather not as I have lots of 25mm

2. Changing another board and all the cables are rear entry including tails.

Anyone see any problem cutting a big square cutout at the back for the cables and tails

Normally I use a stuffing gland at the bottom to hold the tails still

Only thought is the tails are free to move about in free air not that there should be movement but I carnt think how to secure them when they are coming in from behind.

Not enough slack to put a stuffing gland at the back and tighten and place the board to the wall

The current board has them like this floating about.

Cheers
If the supply is 10mm2 can't see the need to upgrade the tails at all
 
Wondering what size main fuse protecting those 10mm singles?
usually about 2 " long and 7/8" thick.

well, you said size, not rating. :D:D:D
 
Just upgrading the tails as it's a pet hate of mine to see a new shiney consumer unit fitted and the old scruffy tails left in place. I always replace the tails when doing a board swap.

I don't have any 16mm DI tails but have 25mm so asking what people's thoughts were as to replacing them with bigger tails and not upgrading the bonding. Don't think it needs to be done as the incoming supply singles are what I think are 10mm in conduit.

Supply type is tns at the main incoming position and there is a separate 10mm earth cable in the conduit which terminates in an earth block next to the meter in the flat.
 
You have a TNS supply of unknown rating but using 10mm² incoming conductors to the meter and 16mm² from meter to board, the bonding is 6mm².
You wish to change the 16mm² tails from meter to board.

There is no reason to do this based on the information you have given but then again there is no electrical problem with changing them to 25mm², there is only the legal problem of removing the meter seals to do this.
The minimum bonding size is 6mm² so this is compliant and does not need changing.

Board 2
You wish to bring in all cables from the rear of the board.
This is a common and even often recommended means of bringing cables into a board so that there is no risk of penetration through accessible surfaces.
If you have concerns about the movement of tails then you could just bring them in through a separate hole that is sufficiently sized to hold the tails steady, but do protect the tails from the edges of the hole with a grommet or strip. Using a membrane grommet may help to hold them in place.
 

Reply to Couple of questions just run by my thoughts in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
I went with a partner. We're able to support each other and take time off knowing the other is at the helm. We split all profit 50/50 whether we...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top