CPC/Earth feed to Light Switch Back Box | Page 2 | on ElectriciansForums

Discuss CPC/Earth feed to Light Switch Back Box in the UK Electrical Forum area at ElectriciansForums.net

B

BettyBoop44

Hi
Just a bit of info required , just been checking all over the house checking for a earth feed to light fittings and switches , ( a friend informed yesterday that there friend have more or less sold there house , but an electrcal inspection has come up with no cpc to all the light switches ) .
I have found 3 light switch back boxes that do not have a earth feed to them , now the question is can I fit a plastic box inplace of the metal one that is in there and not need a earth feed to them ! .
All the light fittings have a earth feed to them ! , every circuit in the house is protected by a RCD .
cheers
BB
 
I assume these are flush to the wall boxes and plastic isn't ideal for this. Do the existing boxes have plastic lugs for the cover screws.

Good point. One of the common issues with light switches is the screws from the face plate being long and puncturing the wires behind. Potentially leaving a live screw head.
A plastic push in cover for each screw helps reduce that risk. Also taking care of the position of the cables as the face plate closes up and the length of the securing screws helps.
 
If the back box and light switch are both non metallic then no CPC is required.
However care must be taken that a later owner doesn't add metal faced switches and a risk is created. We don't rely on RCD for protection as they can fail.
You could leave a note in the plastic backbox as a reminder that no CPC is present and no metal switches to be installed as a sort of gift to the next owner.
Earthing may not be needed, but cpcs need to be present regardless
 
Hi
Thanks for your reply , I am talking about my house not my friends friends house ! , the feed to the lights were also just 2 core flat , I fit a cpc to them a long time ago direct from the cpc bonding terminal next to the meter ,but did not think about the light switches , the kitchen and lounge light switches have a cpc they where put in when some workwas done there prob about 5 year ago .

cheers

BB
BB your post has become confusing, what you need is a comprehensive EICR Electrical Installation Condition Report carried out by a competent Electrician, things have become difficult being drip fed information, get a Spark in to do the EICR and go from there.
 
  1. Taken from best practice guide 1 with installation containing no cpc to lights.
    This is regarding a consumer unit change but nevertheless contains some useful information I think.
    Sorry about the quality as it's copied and pasted

    Carry out a continuity test applied between the earthing terminal in the exis ng consumer unit and all Class I light fittings and metal plate accessories.

    If the resistance value is 1 Ω or less, the equipment may be considered to be earthed.
  1. 10.5.3. An insula on resistance test should be applied between the live conductors (line and neutral connected together) and the earthing terminal in the consumer unit, with that terminal connected to the means of earthing.

    The resistance should be at least 1 MΩ.

  2. 10.5.4. An insula on resistance test should be applied between line and neutral connected together
    and the exposed-conduc ve-parts of every Class I lighting and metal switch plate found to not be earthed by the con nuity tes ng described in Sec on 10.5.2.

    The resistance should be at least 1 MΩ.
10.5.5 If the circuit does not ful l the requirements
of either 10.5.3 or 10.5.4. there would be a
risk of electric shock if the circuit were to be re-energised. The customer must be advised in wri ng that this danger exists, and that the circuit must be disconnected from the supply and should not be connected into a new consumer unit.

10.6. If the customer will not agree to the risk assessment as described in Sec on 10.5. being carried out,
they should be advised that a ligh ng circuit having no protec ve conductor that has metal or Class I switches, light ngs or other accessories ed

is poten ally dangerous (and so would warrant a Code C2 classi ca on in an Electrical Installa on Condi on Report).

This will mean that the circuit cannot be connected into a new consumer unit (see Sec on 4.3 of this Guide).

10.7. It should be noted that the protec ve measure double or reinforced insula on is only applicable
to electrical installa ons or circuits therein that are under e ec ve supervision in normal use to ensure that no change is made that would impair the e ec veness of the protec ve measure (regula on 412.1.3). Domes c and similar premises falling within the scope of this Guide cannot be considered to be under e ec ve supervision.
 
OK guys thank you for all your feedback the conclusion they have to have a cpc to each box/switch , there is only 3 walls to chase down other half will not be happy though it has to be done , would not of looked if it was not for the info my friend told me .

thanks again

BB
 
What size cpc and what routing did you take when installing he seperate cpc as there are regulations governing what should be done
Hi
I took a 2.5mm direct from the earth bonding box next to meter ! , I have to also mention that this problem is only on the lower floor switches upstairs are all fine .
ps: what reg is it that covers that ! .
BB
I assume these are flush to the wall boxes and plastic isn't ideal for this. Do the existing boxes have plastic lugs for the cover screws.
Yes.
 
OK guys thank you for all your feedback the conclusion they have to have a cpc to each box/switch , there is only 3 walls to chase down other half will not be happy though it has to be done , would not of looked if it was not for the info my friend told me .

thanks again

BB
And each light point
 
Hi
Thanks for your reply , I am talking about my house not my friends friends house ! , the feed to the lights were also just 2 core flat , I fit a cpc to them a long time ago direct from the cpc bonding terminal next to the meter ,but did not think about the light switches , the kitchen and lounge light switches have a cpc they where put in when some workwas done there prob about 5 year ago .

cheers

BB
What size cpc did you use and why take from a BONDING conductor connection, ?
 
What size cpc did you use and why take from a BONDING conductor connection, ?
it's also an earthing terminal (MET). better would be to connect to the earth bar in the CU in the correct point for the circuit. and, if not mechanically protected, should be min. 4mm, but that's a minor point.
 

Reply to CPC/Earth feed to Light Switch Back Box in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

It's unlikely tht a small domestic garden pump and a single lamp will come anywhere near close to overloading even the smallest (3A) fused spur...
Replies
2
Views
441
Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
672

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top