It is also possible, and not all that uncommon to damage a bit of flex or T&E and only expose the copper of the live conductor.
 
Well you could argue if the conduit was damaged the phase conductor inside could become damaged and a potential electric shock for someone, the supply would not switch off if no other core run alonside it, thats one argument.

That doesn't mean that there is a requirement, however. In fact even with a cpc run alongside the phase conductor there is absolutely no certainty that the phase wouldn't be damaged without creating an earth fault.
 
If it is an EICR then it cannot 'fail' it can merely be found unsatisfactory and a suitable code given.

Is it immediately dangerous?
Is it potentially dangerous?
Does it require improvement?
 
If it is an EICR then it cannot 'fail' it can merely be found unsatisfactory and a suitable code given.

Is it immediately dangerous?
Is it potentially dangerous?
Does it require improvement?

I can't see any breach of the Wiring Regulations unless it was to enter a ferrous enclosure on its own at some point.
 
whether there's a cpc or not, damage could result in exposed live parts without ADS occuring, so what is the point of a cpc running alongside the L conductor? a an;t see any reg, breached whatewver.note in the comments sesction is all i'd put, just to show that i'd spotted it. c
 
this was my initial point of view. I suppose you could argue that you are increasing the protection even though it may not actually work in practice. I have read through section 4 quickly but I just to tired to take it in. have a read when a bit fresher.
 
If you believe that it is likely to suffer damage then perhaps pvc conduit is not the correct containment rather than wanting a cpc which is not required and would not afford any protection.
 
If it doesn't work in practice then you aren't achieving anything.

If you are going to put this down as an observation requiring any action on an EICR then you need to be able to justify it in the regulations. There is no regulation requiring a cpc to be run alongside every conductor, only one that requires the cpc to be contained within the same wiring system.
 
I can't see any breach of the Wiring Regulations unless it was to enter a ferrous enclosure on its own at some point.
It does enter the light fitting which is ferrous but as I said earlier all other points are earthed, so a short there would result in the protective device tripping.
 
Only if it entered the fitting through a different hole to the CPC and neutral.

I combed through my local SA regs just out of interest and there's also nothing that specifically forbids a single live insulated conductor in its own conduit unless you can class conduit as a sheath as well as containment.
 
It's a requirement of the Regulations that all conductors (including the CPC) of a circuit a within the same ferrous magnetic containment (if used).
As this conductor is not within a ferrous magnetic containment it is not required to be within the same containment as any other circuit conductor.
No it does not require another CPC to be run with it either.
 

Reply to cpc in pvc conduit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
529
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
982
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
916

Similar threads

  • Question
Yes, supply via buried SWA from the main dwelling into new CU. The main house is TT. New CU to have RCBO on all circuits. The workshop area will...
Replies
3
Views
290
Thanks for the help. I’ll measure it up and get something like this...
2
Replies
17
Views
716

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top