Hi all, I'm not so familiar with pvc conduit having used it very little in the past. However, I have a small workshop/man-cave to wire, it is attached to a small domestic dwelling. I need to wire this part using 20mm conduit.
I have a few questions:
1: Am I right in thinking I can wire multiple circuits together in the same conduit? (ie socket outlets and lighting)
2: Can I use a single cpc for all of these circuits or is it best practice to run separate?
3: If conduit is connected in and out of a socket outlet back-box, can other circuit conductors (ie for lighting) run through that back-box?
Is there a CU going in the garage ?
What earthing arrangement ?
Can you give some more info on the intended layout ?
Supply cable, rcd etc ?
I assume you're going to use single cables and not T&E.
1. Yes.
2. Yes but it needs sizing accordingly.
3. Yes but makes future maintenance difficult, not something I would do.
Reactions: Colin33
Yes, supply via buried SWA from the main dwelling into new CU. The main house is TT. New CU to have RCBO on all circuits. The workshop area will have a lighting circuit, and two radial socket circuits in pvc conduit. The separate 'living area' in this building will have lighting circuit, water heating, and a ring final, a tiny bit of UFH and all in twin/earth buried in the studwork.