Crabtree RCCB not tripping -help! | on ElectriciansForums

Discuss Crabtree RCCB not tripping -help! in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jun 12, 2017
Messages
313
Reaction score
289
Location
Sheffield
[ElectriciansForums.net] Crabtree RCCB not tripping -help!


Hi all.

So the Crabtree old style in my hand failed the I delta n test (times 1). But passed the 5 times test.

So I have replaced it with the one in the board. Supposedly reconditioned - and that’s failing both tests but mechanical works.

I am wondering if I am missing something here with my testing.

I am testing through a socket outlet.

Anyone any ideas other than replace with new?
 
Have you checked for N-E faults? These can interfere with both MFT tests and the operation of the test button.
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
 
Thanks Wilco.

I certainly considered not swapping out the original - seeing as it passed the 5 times test - as as you say - is only for additional protection.

I’ve just swapped it out again - and it’s now working.

But - when I tested at the socket outlet - no joy - but tested at the board (to be honest) - and it’s fine.

I’d like to get my head round what’s gone on here.

Best get back to work.....
 
Hi Marcus - a couple of things, apologies if you've already done these :) .
Test with nothing on the outgoing side of RCD.
Confirm tester set to AC and batteries are good.
Target for 1 times with BS4293 is 200ms.
If the RCD is needed for additional protection as per Reg 531.3.6 it turns out that BS4293 devices aren't mentioned on the list anymore. But guidance below states as long as 5 times meets 40ms then it's ok to continue to use the BS4293 device.
http://www.elecsa.co.uk/Documents/Contractor-Documents/Pocket-Guides/Pocket-Guide-25.aspx
That handbook is out of date now.
 

Reply to Crabtree RCCB not tripping -help! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top