Hi all.
So the Crabtree old style in my hand failed the I delta n test (times 1). But passed the 5 times test.
So I have replaced it with the one in the board. Supposedly reconditioned - and that’s failing both tests but mechanical works.
I am wondering if I am missing something here with my testing.
I am testing through a socket outlet.
Anyone any ideas other than replace with new?
Thanks for clarifying. I agree on their use as you've said, for what it's worth
.
Reply to Crabtree RCCB not tripping -help! in the UK Electrical Forum area at ElectriciansForums.net
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
Good to know thanks, one can never have enough places to source parts from!
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
much more information required.
Is the supply to the first building a DNO supply or a sub main cable from another building ?
if it is a sub main...
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...