Gravid

-
Arms
Joined
Jan 5, 2009
Messages
342
Reaction score
34
Hey up, I understand that if disconection times can be met there's no need for supplementry bonding,

but is it still necessary to cross bond say pipes in an immersion heater cupboard or underneath a boiler?

I don't mean coming off a lighting circuit with 4mm, but just linking them together with 4mm. Was

this ever a requirement in the regs ? Cheers.
 
So reg 411.3.1.2 about covers it then, protective equipotential bonding including other installation pipework and

ducting. So you are supposed to bond all the pipes in that situation regardless of disconnection times.
 
411.3.2 is your Main equipotential bonding where the servives enter the building that HAS to be bonded.
At other pipework is Suplimentary Bonding which is different and is covered in section 415.2

Have a look at Fig 2.1 0n page 32 of the regs which may explain the 4 different names for protective conductors and what they mean.
 
Oh aye yeah, my mistake, thats really meant for Oil or another incomming service.

In fig 2.1 its saying where required to supplementry bond exposed conductive parts, i thought boiler/immersion pipes

where extraneous. In 4.6 of the OSG it says where requirements have been met ( does this mean ADS? ) theres no

need to bond. Probably confusing myself thanks any way.
 
i have quotes from the 17th regs book not the OSg

Yes ADS as well as R,50 /Ia where Ia is the rated current of the overcurrent device or the tripping current of the RCD,RCBO
As the pipework is normally linked to a boiler then it is tied to the electrical system so therefore exposed conductive parts. the only difference my be something like a standpipe in a caravan park.
 
Last edited:
Ok, but i still can't find anything that says you have to do this, I mean if your main bonds are in place at your incoming

water and gas/oil why do you bother linking random pipes with 4mm? Just i've worked with people who do and people

who don't and was looking into whether this was a reg.
 
It is not a clear Yes or No it all depens on the installation.

Using the Long lead method from the main earth terminal test to exposed conductive parts in the installatio. In this case the Pipework below the boiler. If the resistance is less then 50/ Ia then no bonding is requierd as you have the disconnection time as well as no more than 50V on the exposed metal. If it is higher then you have to install suplimentary bonding.

The Electrical safety council say as a rule less then 0.5 ohms. As most houses have a hundred amp main incommer so 50/100 =0.5 so your covered.

hope this makes sence its is all explained in the Reg 415.2. also read reg 544
 
Last edited:
This is what the ESC & others have to say about supplementary bonding at boilers:

Does boiler pipework need to have additional equipotential bonding for electrical safety reasons?

There is no specific requirement in the Regulations for boiler pipework to be supplementary bonded. However, such bonding may be called for in the boiler manufacturer’s instructions, in which case BS 7671 requires those instructions to be followed (Regulation 510.2 refers). Any stated requirement for additional bonding that is considered to be unnecessary should be queried with the manufacturer concerned, and amended installation instructions requested.

(See reg no 411.3.3)
New or Rewired Domestic and Similar Installations, Question 6
 
I thought it was 0.05 ohms mate... someone poelase correct me if wrong but im pretty sure its gotta be 0.05 ohms or less.

Cheers

No need to correct you matey, 0.05 it is.;)

Check GN3 for confirmation.

Scottie is also right as it is to keep the touch voltage thay may flow under fault coditions below 50V.
 
I always thought the max resistance was 0.05 ohms not 0.5 ohms and Ia in the formula related to
the nominal rated tripping current of an rcd/rcbo and the current that needed to flow to cause operation
of a device such as a fuse/mcb in a given time such as 0.4 seconds and not the nominal rated current of the device.
 

Reply to Cross Bonding in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
327
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
303
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
365

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
450

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top