Due to a burnt out 80a rcd on a wylex split board consumer unit, the consumer unit now only has one 80a rcd which all circuits (mcbs) are wired to, so a new 80a rcd has been bought to reinstate the split board. The issue is that the original live and neutral cables that linked the mcbs together have mistakenly been thrown out what is the actually csa if these cables? I don't want to obviously buy an old consumer unit off eBay just for these two short cables but I have found a supplier of various sized awg cables and I'm guessing these should do the job of the original linked cables? Any advice is appreciated
 
Not used Wylex boards are they solid links or flex type cables ?
But as long as the cable can take 80amps ie 16mm and above it wouldn't matter.

Thanks for your reply bryanh, they are the stranded type that run from the neutral block to the fuses etc the strands are normally crimped by the manufacturer into a long metal point for ease of use when terminating into the rcd itself.
 
buy a plastic wylex split load board with 2 RCDs, no MCBs. pinch the tails . cost is peanuts and you'll have 2 RCDs for stock.
 
MK Split Load Kit - Toolstation

You can pick up cable kits for a few quid too. Not sure of the length, but maybe Wylex do a similar kit to match ?

Thanks folks for your advice. I tried to find a cheap wylex split load board but couldn't find one cheap enough to justify the situation so I headed to screwfix and got an MK split load kit which was about 6 quid and includes 2 neutrals and a live, perfect!
 

Reply to csa of wylex rcd live and neutral link cables in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top