ct clamps too close together? | on ElectriciansForums

Discuss ct clamps too close together? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Joined
Dec 7, 2017
Messages
119
Reaction score
14
Location
wellingborough
Hi,

I have a 16kW array fed to my cu via 3 - 5kW solis inverters. I have a 4kW export limit so each inverter has a ct clamp. The 3 clamps are together on my main incoming cable.

Is it ok to have these 3 clamps touching each other?
How is it decided which inverter to shut down?

We have a lot of tripping issues, the system was installed incorrectly & still doesn't work properly. Could there be interference between the clamps & would them constantly turning on and off randomly be causing the tripping.

Thanks in advance

Greg Webb
 
Well,
Each one will be indepently deciding, I am pushing out too much, need to to turn down the wick. Depending on the control loop and the nature of the local load this could cause instablitlies. You might also want to check the local supply voltage to see if you are tripping on over voltage.
 
Last edited:
Hi - just trying to understand how the 3 invertors can be limited to achieve 4kW total system output. Are you saying that each of the 3 invertors has their own CT and is independently trying to limit to 4kW? (likely result today being 12kW ...). Or if not, how does each know what the other is doing? If you've a circuit diagram and pics it might help :) .
 
Hi - just trying to understand how the 3 invertors can be limited to achieve 4kW total system output. Are you saying that each of the 3 invertors has their own CT and is independently trying to limit to 4kW? (likely result today being 12kW ...). Or if not, how does each know what the other is doing? If you've a circuit diagram and pics it might help :) .

Thanks for the reply, I'm not an electrician so I can't say how each one is set up. I strongly believe that each one is set to 4kW so once this is reached one of them will turn down or off, if it still is over 4kW then another will turn down or off. I am positive they are all set up the same.
 
here is a pic of all 3 ct clamps in a row on the incoming main cable.

[ElectriciansForums.net] ct clamps too close together?
 
Ok a picture paints 1000 words, they need to be clamped round 1 of the 4 cables going into the bottom of the electricty meter!

Thanks, I will try that, it just seems that the clamps will then simply be the other side of the main incoming fuse. Wouldn't they still be sensing the reverse flow to the grid in either position? I am thinking of using the brown cable from the bottom of the fuse to the meter. See pic attached.

[ElectriciansForums.net] ct clamps too close together?
 
Was this a DIY installation ?

No a local company put it in last September and I had loads of problems far too many to list here but included no drip loops - ct clamps on the wrong cable - meter frying - loads of "spare" holes in roof, new supply cable from grid - earthing problems etccccccc.

p.s just tripped again!
 

Reply to ct clamps too close together? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
706
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top